For those interested in the UFC 3-600-01 design approaches, I received
an informal opinion on the appropriate method to apply NFPA 13R
calculation methods.  Of course this is based on using NFPA 13R for the
correct buildings in the first place.

1.  Inside the dwelling unit use NFPA 13R.
2.  Outside the dwelling unit use NFPA 13R and any references to NFPA
13.
3.  A four head corridor calculation in the dwelling unit is acceptable
(see NFPA 13, Figure A.11.3.1.2).
4.  No hose stream is necessary.

Last, no fire department connection is required.

The project RFP or project plans and specs could overrule any or all of
the above and local installation guidelines might also differ.

Bill Brooks