And if you tried some of that in Southwest Div you'd be laughed out of
the building.   They generally require arbitrarily doubled design areas,
so out here it's an 8-sprinkler design area - corridor or dwelling unit
using residential sprinklers - or .10/3000 sf and it's up to the FPE
doing the review whether or not you can observe a dwelling unit as a
"largest room" design area; hose stream of 100 GPM is required for
residential and 250 for light hazard (500 for ordinary); FDC is
required.   AND, if it's a multi-story building then floor controls are
required and if sprinklers are combined with standpipes then they must
be looped, but calculations performed only on the more demanding
straight path.

And you have to do the calculations whilst balanced on your left leg
(right leg if you're left-handed) and wearing your cap backwards and
shouting, "Don't worry about costs, the money grows on trees!" 

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Saturday, June 27, 2009 1:21 PM
To: [email protected]
Subject: DoD UFC - 13R System Design (Update)

For those interested in the UFC 3-600-01 design approaches, I received
an informal opinion on the appropriate method to apply NFPA 13R
calculation methods.  Of course this is based on using NFPA 13R for the
correct buildings in the first place.

1.  Inside the dwelling unit use NFPA 13R.
2.  Outside the dwelling unit use NFPA 13R and any references to NFPA
13.
3.  A four head corridor calculation in the dwelling unit is acceptable
(see NFPA 13, Figure A.11.3.1.2).
4.  No hose stream is necessary.

Last, no fire department connection is required.

The project RFP or project plans and specs could overrule any or all of
the above and local installation guidelines might also differ.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4193 (20090626) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4194 (20090628) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to