In PACDIV it's 13 only! No reduction for QR, 3000 Sf min. design area. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Sunday, June 28, 2009 4:18 PM To: [email protected] Subject: RE: DOD UFC - 13R System Design (Update) And if you tried some of that in Southwest Div you'd be laughed out of the building. They generally require arbitrarily doubled design areas, so out here it's an 8-sprinkler design area - corridor or dwelling unit using residential sprinklers - or .10/3000 sf and it's up to the FPE doing the review whether or not you can observe a dwelling unit as a "largest room" design area; hose stream of 100 GPM is required for residential and 250 for light hazard (500 for ordinary); FDC is required. AND, if it's a multi-story building then floor controls are required and if sprinklers are combined with standpipes then they must be looped, but calculations performed only on the more demanding straight path. And you have to do the calculations whilst balanced on your left leg (right leg if you're left-handed) and wearing your cap backwards and shouting, "Don't worry about costs, the money grows on trees!" Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Saturday, June 27, 2009 1:21 PM To: [email protected] Subject: DoD UFC - 13R System Design (Update) For those interested in the UFC 3-600-01 design approaches, I received an informal opinion on the appropriate method to apply NFPA 13R calculation methods. Of course this is based on using NFPA 13R for the correct buildings in the first place. 1. Inside the dwelling unit use NFPA 13R. 2. Outside the dwelling unit use NFPA 13R and any references to NFPA 13. 3. A four head corridor calculation in the dwelling unit is acceptable (see NFPA 13, Figure A.11.3.1.2). 4. No hose stream is necessary. Last, no fire department connection is required. The project RFP or project plans and specs could overrule any or all of the above and local installation guidelines might also differ. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4193 (20090626) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4194 (20090628) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)