Yeah...what Craig said. I did not mean to discourage anyone.
I was only thinking that this install does not conform to NFPA 13 and 
violates some rules of installation I have learned and obeyed for many 
years.

BTW: I was not thinking of heat collectors (which do not exist, right?) but 
proximity to ceiling or overhangs, etc...

Thomas Watt
Overqualified laid-off again Foreman/fitter
----- Original Message ----- 
From: <[email protected]>
To: <[email protected]>
Sent: Monday, July 06, 2009 10:39 AM
Subject: RE: Membrane dome in Sprinkler Age


> Don't despair over the ramblings and musings of those who have seen the 
> picture of the installation. It's just that we in the industry look at 
> something like that and try to figure out the reasoning of the one who 
> came up with the design.   The questions aren't necessarily pointed to 
> you, it's just more like thinking out loud.
>
> Thanks for sharing,
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Stewart 
> Kidd
> Sent: Monday, July 06, 2009 10:16 AM
> To: [email protected]
> Subject: Re: Membrane dome in Sprinkler Age
>
> I'm beginning to regret even mentioning the premises.
>
> I have no information at all on the system or the assumptions behind them. 
> I understand that the the protection was installed voluntarily (ie there 
> was no legal requirement to provide protection) when the change of use 
> took place - the skating rink was not previously protected. The photo was 
> taken more than 10/12 years ago and I'm not even sure if the premises are 
> still used for retailing.
>
> Can't help further, sorry
>
> Stewart
> On 6 Jul 2009, at 14:22, John Drucker wrote:
>
>> So Arup's determination assures that the forementioned sprinkler
>> protection will operate and control the fire matching the performance
>> of a typical system where a roof or ceiling barrier is present ?.
>>
>> Seems to me the concern would be uncontrolled fire spread to adjacent
>> contents.
>>
>> John Drucker Jr.
>> Fire Protection Subcode Official
>> Borough of Red Bank, NJ
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Stewart
>> Kidd
>> Sent: Monday, July 06, 2009 8:54 AM
>> To: [email protected]
>> Subject: Re: Membrane dome in Sprinkler Age
>>
>> Thomas
>>
>> This is not one of my jobs - I have done an insurance review but was
>> not involved the system design and installation.
>>
>> Given the height of the heads and the fuel load and likely fire spread
>> scenario I believe the fire strategy report prepared by Arup Fire
>> decided that collectors were unnecessary.
>>
>> Regards
>>
>> Stewart
>>
>>
>> On 6 Jul 2009, at 00:10, Thomas Watt wrote:
>>
>>> Wow...no heat collection necessary eh?
>>>
>>>
>>> ----- Original Message -----
>>> From: "Stewart Kidd" <[email protected]>
>>> To: <[email protected]>
>>> Sent: Sunday, July 05, 2009 6:30 AM
>>> Subject: Re: Membrane dome in Sprinkler Age
>>>
>>>
>>>> Can't post the file due to restrictions on the size of submissions.
>>>> Happy to send it to anyone who wants.
>>>>
>>>> Stewart
>>>> On 5 Jul 2009, at 10:44, Haji, Jaber M wrote:
>>>>
>>>>> Pls let's share the picture. Thanks in advance.
>>>>>
>>>>> -----Original Message-----
>>>>> From: [email protected]
>>>>> [mailto:[email protected]
>>>>> ] On Behalf Of Stewart Kidd
>>>>> Sent: Sunday, July 05, 2009 11:58 AM
>>>>> To: [email protected]
>>>>> Subject: Re: Membrane dome in Sprinkler Age
>>>>>
>>>>> Frans
>>>>>
>>>>> Can't recall the article but there is a UK shopping centre
>>>>> (converted from a skating rink) which is sprinkler protected using
>>>>> free standing posts each with three or four arms containing
>>>>> sprinkler heads.  I'll send you a picture off-line.
>>>>>
>>>>> Regards
>>>>>
>>>>> Stewart
>>>>>
>>>>> On 5 Jul 2009, at 01:19, Frans Stoop wrote:
>>>>>
>>>>>> Dear colleagues,
>>>>>>
>>>>>> If my memory serves me right, there was an article in Sprinkler
>>>>>> Age
>>
>>>>>> some years ago about how a contractor installed water monitors
>>>>>> inside a dome structure.
>>>>>> Installing sprinklers was impossible because the main structure
>>>>>> was
>>
>>>>>> only an (inflatable?) membrane.
>>>>>>
>>>>>> I tried to retrieve that article by digging through old years of
>>>>>> Sprinkler Age but unfortunately I couldn't find it.
>>>>>> Or was it in Fire Journal?
>>>>>>
>>>>>> Does anyone of you happens to remember that article and can point
>>>>>> me to the right year and number?
>>>>>>
>>>>>> Frans Stoop
>>>>>> TOS architecture & fire protection Netherlands
>>>>>> <[email protected]> Tel. +31-24-324 0112
>>>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>> For Technical Assistance, send an email to:
>>>>>> [email protected]
>>>>>>
>>>>>> To Unsubscribe, send an email
>>>>>> to:[email protected]
>>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>> For Technical Assistance, send an email to:
>>>>> [email protected]
>>>>>
>>>>> To Unsubscribe, send an email
>>>>> to:[email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>> The contents of this email, including all related responses, files
>>>>> and attachments transmitted with it (collectively referred to as
>>>>> "this Email"), are intended solely for the use of the individual/
>>>>> entity to whom/which they are addressed, and may contain
>>>>> confidential and/or legally privileged information. This Email may
>>>>> not be disclosed or forwarded to anyone else without authorization
>>>>> from the originator of this Email. If you have received this Email
>>>>> in error, please notify the sender immediately and delete all
>>>>> copies
>>
>>>>> from your system. Please note that the views or opinions presented
>>>>> in this Email are those of the author and may not necessarily
>>>>> represent those of Saudi Aramco. The recipient should check this
>>>>> Email and any attachments for the presence of any viruses. Saudi
>>>>> Aramco accepts no liability for any damage caused by any virus/
>>>>> error
>>
>>>>> transmitted by this Email.
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>> For Technical Assistance, send an email to:
>>>>> [email protected]
>>>>>
>>>>> To Unsubscribe, send an email
>>>>> to:[email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> For Technical Assistance, send an email to:
>>>> [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>>> to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>
>>>
>>> ---------------------------------------------------------------------
>>> -
>>> ----------
>>>
>>>
>>>
>>> Internal Virus Database is out of date.
>>> Checked by AVG - www.avg.com
>>> Version: 8.5.374 / Virus Database: 270.12.69/2176 - Release Date:
>>> 06/14/09
>>> 17:54:00
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to:
>>> [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to:
>> [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> CONFIDENTIAL AND PROPRIETARY:
>> This email message is intended only for the use of the individual or
>> entity to which it is addressed and may contain information that is
>> privileged and confidential, nor is it, unless specifically stated,
>> intended to be relied upon by any person or persons other than the
>> individual or entity named above and no warranties or representations
>> are made or intended to persons or entities not named above.  If the
>> reader is not the intended recipient, you are hereby notified that any
>> dissemination, distribution or copying of this communication is
>> strictly prohibited.  If you have received this communication in
>> error, please notify us immediately by telephone, return this message
>> to the address above and delete all copies.  Thank you.
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to:
>> [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)


--------------------------------------------------------------------------------



Internal Virus Database is out of date.
Checked by AVG - www.avg.com
Version: 8.5.374 / Virus Database: 270.12.69/2176 - Release Date: 06/14/09 
17:54:00

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to