Let's start with the elevator code ASME A17.1 reference to it does not
appear in 13D, nor does 13D reference 13 when 13D does not apply. So this is
an area where the 13D committee needs to make some sort of a guide. 

Many of the home elevators are not from Otis or Shindler or any other major
MFG, and don't meet the same standards as commercial residential elevators.
Many are (MRL) machine room less, with the motors on top or under the cab.
There are climbers, fiction climbers and belt climbers as well as hydraulic.
The smoke detector at the top of shaft is building code required, but it's
not interfaced with elevator controls. Some shafts are vented, and some are
not as the elevator moves slow enough to allow air to move around the cab
without compressing it. Vented shafts present the freeze issue for any
sprinklers. Dry  sprinklers could allow for this, but they are not
residential listed. Again more guidance is needed from 13D committee.
Currently we protect "fueled Heat producing appliances within concealed
spaces" these are not fueled, or heat producing as part of their function.
If we start protecting non fueled appliances, will we then protect bathroom
exhaust fans? Even if they have a heater element or infrared lamps? Small
pumps, or fan coils?

I think I remember something in a proposal for 13D 2010 about elevators, but
I'll have to look it up. 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Friday, September 11, 2009 4:58 PM
To: [email protected]
Subject: 13D Elevator

Next question; 13D allows for the elimination of the sprinkler in the
elevator equipment room, though I'm including one on this project since the
room is designated as equipment/storage.  I'm assuming that I will need a
sprinkler at the top and bottom of the elevator shaft since it is
constructed of wood.  The trouble that I foresee here is that there is only
18" between the finished floor and the bottom of the elevator pit.  Will
this give me enough room to install a sprinkler?  If there is a smoke at the
top of the shaft can I eliminate that sprinkler?  Or, should I eliminate the
pit sprinkler and keep the upper sprinkler?  Or, is there another solution
that someone else has used?

Thanks again,
      
Bob Knight, CET
1660 Hill Rd
Melba, Idaho 83641
(208) 318-3057
(208) 495-2057 fax
[email protected]
www.firebyknight.com

-------------- next part --------------

No virus found in this outgoing message.
Checked by AVG - www.avg.com
Version: 8.5.409 / Virus Database: 270.13.91/2363 - Release Date: 09/11/09
09:15:00 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to