There is a discussion group for AWWA engineers.
I would post this on there as waterworks contractors probably know the 
answer.


Forest Wilson

Project Manager
Cherokee Fire Protection Co.
3195 Dayton Xenia Rd Ste 900
Dayton OH 45434

ph: 937-376-2333
fx: 614-455-4324
cell: 937-307-5647


.



Visit our blog: www.cherokee-fire.blogspot.com







NOTICE: The information contained in this email is intended to be 
solely for the use of the named individual or entity to which it is 
directed and may contain information that is privileged or otherwise 
confidential. It is not intended for transmission to, or receipt by, 
anyone other than the named addressee (or a person authorized to 
deliver it to the named addressee). It should not be copied or 
forwarded to any unauthorized persons. If you have received this 
electronic mail transmission in error, please delete it from your 
system without copying or forwarding it, and notify the sender of the 
error by reply email or by calling Cherokee Fire Protection Co. at 
888-347-3079 toll free.


-----Original Message-----
From: Autry, David <[email protected]>
To: [email protected] <[email protected]>
Sent: Wed, 23 Sep 2009 15:41:07 -0500
Subject: RE: Post Indicators

Understand.

If you do find and go with some sort of gear arrangement, it might take 
more than 5 seconds. :-)

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [email protected]


-----Original Message-----
 From: [email protected] 
[mailto:[email protected]] On Behalf Of Hinson, 
Ryan
Sent: Wednesday, September 23, 2009 3:38 PM
To: [email protected]
Subject: RE: Post Indicators

We have included that argument among others.  This is not the first
issue we've had with them regarding what the codes and standards as they
are their own approving jurisdiction.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Autry,
David
Sent: Wednesday, September 23, 2009 3:33 PM
To: [email protected]
Subject: RE: Post Indicators

Can't use ball valves per NFPA 24 (2002, Edition) 6.1.2

Indicating valves shall not close in less than 5 seconds when operated
at maximum possible speed from the fully open position.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Hinson,
Ryan
Sent: Wednesday, September 23, 2009 3:27 PM
To: [email protected]
Subject: Post Indicators

Does anyone know of a post indicator that can be used in conjunction
with a 12" ball valve installed below grade?  I've been trying to find
one at the request of a customer for use as control valves for the
underground firewater piping of an industrial facility.  We've gone
around and around ad nauseam but they don't want butterfly or gate
valves because in their words they, "don't want to dig up the valve when
it no longer seals".  Ball valves that size normally require a ~3' long
handle and show the handle almost directly fastened to the valve body
itself.  Gearboxes could be used at valve level, but I still need to
extend the handle of the gearbox above grade in such a way as to
indicate the valve position.  Anyone out there with any experience with
this scenario?



Ryan L. Hinson, EIT, NICET III

Fire Protection Systems Designer, Aviation and Facilities Group

Minneapolis-St. Paul Office

Burns & McDonnell

8201 Norman Center Drive, Suite 300

Bloomington, MN 55437

Direct: 952-656-6003 Ext 3662

Fax: 952-229-2923

www.burnsmcd.com <BLOCKED::www.burnsmcd.com>





Proud to be one of FORTUNE's 100 Best Companies To Work For



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email 
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email 
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to