Wouldn't the insurance carrier also have some interest in this procedure?Seems
you wouild be giving  his lawyers a chance for a "Field Day" in court if a 
failure
occured and it was learned that proper maintenance as directed by the 
standard had not been conducted.Just a thought.


---- David de Vries <[email protected]> wrote: 
> Seems I recall that this type issue has come up in the past -- perhaps it was 
> smoke alarms or heat detectors, or some such.  In any event the owner was VA 
> or other large, multi-building owner and they developed a program that was 
> statistically sound in reducing the frequency of testing without 
> substantially altering the reliability of the system.  The concept went thru 
> an NFPA committee (wish I could remember which) and was accepted.  Closest 
> thing I can find in 25 is Section 1.3 and A.1.3.
>  
> My suggestions (as long as the full 10 minute run time is not showing signs 
> of overheating or unusual noise/vibration):
>  
> -  talk to the owner about budgeting for a pump replacement in next few years,
> -  continue doing weekly starts, but cut the run time to a few minutes, just 
> long enough so that pressure is built up and the seals are wetted (determine 
> the length of run time based on those criteria and anything else suggested by 
> forum members - Tom D., George C., Thom M. etc. thoughts??),
> -  do the full 10 minute run test once a month,
> -  document, document, document,
> -  promptly repair any anamoly that shows up.
>  
> If the weekly test run time gets down to 1 to 2 minutes 3 times per month, 
> the total time for the month has been reduced by more than half and may 
> extend the life of the pump.  Problems with starting on pressure drop, not 
> running at all, not building up pressure, etc. will be apparent even with the 
> reduced run time.
>  
> BTW I cannot tell you how many owners I have come across who rely solely on 
> the annual pump test.  It does not run the rest of the year.  When I ask them 
> for records of their weekly tests, I get "huhhh???" in response.
>  
> Dave 
> 
> David A. de Vries, P.E., CSP 
> Firetech Engineering Incorporated 
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to