What type of vibration readings do you take and how do you do it? I have
never done vibration readings. Is there a standard that could be referenced?

Jim Toth
_________________________________________________

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of MOWLE
Kevin(K) - BRUCE POWER
Sent: Friday, October 02, 2009 11:03 AM
To: [email protected]
Cc: [email protected]
Subject: RE: Fire Pump Testing NFPA 25 requirements

Hi Tom,

Our firewater pumps are tested monthly.
Each pump is valved individually to the test header then a low water
pressure signal is created by opening the discharge valves on the test
header.
The suction and discharge pressures are recorded.
The motor and pump bearing temperatures are checked near the end of the run.
Due to the pipe/valve configuration the labour for this work takes two
people 3 to 4 hours each.

For the annual tests we utilize 6 hosemonsters to measure the flows
progressing from no-flow to all 6 monsters. (a LOT of water) We also take
vibration readings while running.
The results recorded and used for trending.

Kevin Mowle
Bruce Power.



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Friday, October 02, 2009 9:54 AM
To: [email protected]
Subject: RE: Fire Pump Testing NFPA 25 requirements

Kevin-
Do you flow water and measure it monthly?  What about annually?  Still on a
14 y.o. standard?
Tom Duross


The National Fire Code of Canada (1995) 6.6.3.3 allows for a monthly run
test for electrically driven pumps.
In the appendix it also states: "Centrifugal fire pumps should not be
operated for prolonged periods under shut-off conditions, that is, with no
water flowing from the system" "because of the excessive wear on impellors
due to the caviation, and on seals and thrust bearings due to the higher
operating pressure and increased vibrations. Water should be discharged from
the system if possible."

Here we run our monthly tests (200hp Aurora 2000 usgpm) through the test
header to confirm proper flow and operation of the pump controllers.

Kevin Mowle
Bruce Power.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
****************************************************************************
**********************
*** The contents of this email and any attachments
*** are confidential and may be privileged.
*** They are intended for the named recipient(s) only.
*** If this message has been delivered to you in error, please reply to the
*** sender to that effect, don?t forward the message to anyone
*** and delete the message from your computer.
*** Thanks for your help, and sorry for the inconvenience. (BP)
****************************************************************************
**********************


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to