Travis,

I've always looked at "limited combustible" as a subjective term. You 
know what isn't, but not sure what is. If you have 2x's at 16" oc all 
over the place, chances are it isn't "limited combustible". If they 
used a few pieces of wood to support and ceiling fixture in an 
otherwise N/C space, that would be limited. I usually work with the 
AHJ to come up with a consensus. That also stops a lot of arguments.

Todd

At 03:10 PM 9/30/2009, you wrote:
>We have a hotel designed per NFPA 13.  The 2nd floor is concrete.  The
>building plans showed the gyp board ceilings to be framed with non
>combustible channel.  Therefore, the space above the 1st floor ceilings
>would be a non-combustible concealed space.  However, when the fitters
>arrived on site, it was found that the GC has taken it upon himself to frame
>all of the gyp board ceilings / soffits on the first floor with wood.  Would
>this be considered minimal / minor quantities of non structural wood?  What
>is a decent defining factor for minor quantities?  If sprinklers are
>required, the GC realized today that a change order is forth-coming.  It is
>just an issue of scheduling to go back and get the first floor redesigned to
>accomodate the new construction.  This project was also done with CPVC
>piping, so we would have to go with the specially listed concealed space
>sprinklers to protect these areas.
>
>8.15.1.2.1*  Concealed spaces of noncombustible and limited-combustible
>construction with minimal combustible loading having no access shall not
>require sprinkler protection. The space shall be considered a concealed
>space even with small openings such as those used as return air for a
>plenum. (For additional information on combustible loading, see
>A.8.15.1.2.1.)
>
>A.8.15.1.2.1  Minor quantities of combustible materials such as but not
>limited to: cabling, nonmetallic plumbing piping, non-structural wood, etc.
>can be present in concealed spaces constructed of limited or noncombustible
>materials but should not typically be viewed as requiring sprinklers (see
>8.15.1.1). For example, it is not the intent of this section to require
>sprinklers, which would not otherwise be required, in the interstitial space
>of a typical office building solely due to the presence of the usual amount
>of cabling within the space.  The threshold value at which sprinklers become
>necessary in the concealed space is not defined.
>
>Thanks in advance for any help / opinions.
>
>Travis Mack
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to