I agree with Todd if it's the walls = sprinkler all. But I think the question is limited to gyp CIELINGS and SOFFITS. In that case I think '02-8.14.1.5 can help, Localized Protection of Exposed Combustible Construction.
I do think you have to deal with it either way. Unless the area involved is really, really small like a few sq.ft. separated by 20's of feet to the next few sq.ft. IDK? Without seeing it can't advise on the judgment call on how small is small. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, September 30, 2009 3:03 PM To: [email protected] Subject: Re: A.8.15.1.2.1 Travis, I've always looked at "limited combustible" as a subjective term. You know what isn't, but not sure what is. If you have 2x's at 16" oc all over the place, chances are it isn't "limited combustible". If they used a few pieces of wood to support and ceiling fixture in an otherwise N/C space, that would be limited. I usually work with the AHJ to come up with a consensus. That also stops a lot of arguments. Todd At 03:10 PM 9/30/2009, you wrote: >We have a hotel designed per NFPA 13. The 2nd floor is concrete. The >building plans showed the gyp board ceilings to be framed with non >combustible channel. Therefore, the space above the 1st floor ceilings >would be a non-combustible concealed space. However, when the fitters >arrived on site, it was found that the GC has taken it upon himself to frame >all of the gyp board ceilings / soffits on the first floor with wood. Would >this be considered minimal / minor quantities of non structural wood? What >is a decent defining factor for minor quantities? If sprinklers are >required, the GC realized today that a change order is forth-coming. It is >just an issue of scheduling to go back and get the first floor redesigned to >accomodate the new construction. This project was also done with CPVC >piping, so we would have to go with the specially listed concealed space >sprinklers to protect these areas. > >8.15.1.2.1* Concealed spaces of noncombustible and limited-combustible >construction with minimal combustible loading having no access shall not >require sprinkler protection. The space shall be considered a concealed >space even with small openings such as those used as return air for a >plenum. (For additional information on combustible loading, see >A.8.15.1.2.1.) > >A.8.15.1.2.1 Minor quantities of combustible materials such as but not >limited to: cabling, nonmetallic plumbing piping, non-structural wood, etc. >can be present in concealed spaces constructed of limited or noncombustible >materials but should not typically be viewed as requiring sprinklers (see >8.15.1.1). For example, it is not the intent of this section to require >sprinklers, which would not otherwise be required, in the interstitial space >of a typical office building solely due to the presence of the usual amount >of cabling within the space. The threshold value at which sprinklers become >necessary in the concealed space is not defined. > >Thanks in advance for any help / opinions. > >Travis Mack >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)