CAUTION:  The current NFPA 13 does define "limited combustible" with respect
to materials, not quantities or percentage.

Ed Vining



*3.3.13* 
<http://nfpacodesonline.org/a/c.ref/ID00001332264/sec>Limited-Combustible
(Material).
*   Refers to a building construction material not complying with the
definition of noncombustible material that, in the form in which it is used,
has a potential heat value not exceeding 3500 Btu/lb (8141 kJ/kg), where
tested in accordance with NFPA
259<http://nfpacodesonline.org/a/c.ref/NFC259/book>,
*Standard Test Method for Potential Heat of Building Materials*, and
includes either of the following: (1) materials having a structural base of
noncombustible material, with a surfacing not exceeding a thickness of
1/8in. (3.2 mm) that has a flame spread index not greater than 50; or
(2)
materials, in the form and thickness used, having neither a flame spread
index greater than 25 nor evidence of continued progressive combustion, and
of such composition that surfaces that would be exposed by cutting through
the material on any plane would have neither a flame spread index greater
than 25 nor evidence of continued progressive combustion, when tested in
accordance with ASTM E 84, *Standard Test Method of Surface Burning *

On Wed, Sep 30, 2009 at 1:03 PM, Todd Williams <[email protected]> wrote:

> Travis,
>
> I've always looked at "limited combustible" as a subjective term. You
> know what isn't, but not sure what is. If you have 2x's at 16" oc all
> over the place, chances are it isn't "limited combustible". If they
> used a few pieces of wood to support and ceiling fixture in an
> otherwise N/C space, that would be limited. I usually work with the
> AHJ to come up with a consensus. That also stops a lot of arguments.
>
> Todd
>
> At 03:10 PM 9/30/2009, you wrote:
> >We have a hotel designed per NFPA 13.  The 2nd floor is concrete.  The
> >building plans showed the gyp board ceilings to be framed with non
> >combustible channel.  Therefore, the space above the 1st floor ceilings
> >would be a non-combustible concealed space.  However, when the fitters
> >arrived on site, it was found that the GC has taken it upon himself to
> frame
> >all of the gyp board ceilings / soffits on the first floor with wood.
>  Would
> >this be considered minimal / minor quantities of non structural wood?
>  What
> >is a decent defining factor for minor quantities?  If sprinklers are
> >required, the GC realized today that a change order is forth-coming.  It
> is
> >just an issue of scheduling to go back and get the first floor redesigned
> to
> >accomodate the new construction.  This project was also done with CPVC
> >piping, so we would have to go with the specially listed concealed space
> >sprinklers to protect these areas.
> >
> >8.15.1.2.1*  Concealed spaces of noncombustible and limited-combustible
> >construction with minimal combustible loading having no access shall not
> >require sprinkler protection. The space shall be considered a concealed
> >space even with small openings such as those used as return air for a
> >plenum. (For additional information on combustible loading, see
> >A.8.15.1.2.1.)
> >
> >A.8.15.1.2.1  Minor quantities of combustible materials such as but not
> >limited to: cabling, nonmetallic plumbing piping, non-structural wood,
> etc.
> >can be present in concealed spaces constructed of limited or
> noncombustible
> >materials but should not typically be viewed as requiring sprinklers (see
> >8.15.1.1). For example, it is not the intent of this section to require
> >sprinklers, which would not otherwise be required, in the interstitial
> space
> >of a typical office building solely due to the presence of the usual
> amount
> >of cabling within the space.  The threshold value at which sprinklers
> become
> >necessary in the concealed space is not defined.
> >
> >Thanks in advance for any help / opinions.
> >
> >Travis Mack
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email 
> >to:[email protected]<to%[email protected]>
> >(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to