I digitally searched NFPA 13 and FMDS 2-2 and no reference to 30,000 sq ft or 2,800 m2 for anything related to ESFR. 40,000sf (3716m2) for the overall area, 100 sf (9.3m2) for max. ESFR head spacing.
About the closest you get to your 30,000 sf area is listed for extra hazard pipe schedule systems, the limitation is 25,000 sf. In NFPA 13, 2007, see 8.2 Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of sam b Sent: Tuesday, October 20, 2009 8:34 AM To: [email protected] Subject: Re: ESFR - maximum system limit Hii Thaanx dwayne for the quick response. But I still believe I have read somewhere this 2800 m2 limitation. Did google a lott but with no help. :( Does anyone share this doubt? Regards Sam On Mon, Oct 19, 2009 at 2:56 PM, Dewayne Martinez <[email protected]> wrote: > ESFR sprinklers are to be used for storage so the 40,000 SQ FT limit > applies. > Dewayne > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of sam b > Sent: Monday, October 19, 2009 2:54 AM > To: [email protected] > Subject: ESFR - maximum system limit > > Friends, > > Need a small info regarding ESFR sprinkler system. > > What is maximum system area limit for a ESFR sprinkler system? > > I have read somewhere that it is 2800 m2(30,140 ft2).But I am unable > to locate it now. > I searched NFPA 13 but couldnt find it. > > Can anyone confirm whether its the same or is it 40,000 ft2 ( high > piled storage).? > > > Thaanx in advance > > Sam > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%3ASprinklerforum-reques > [email protected]> (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%3ASprinklerforum-reques > [email protected]> (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)