I don't know if this helps but it is a similar discussion

  http://inspector911.com/does-this-meet-code-10/444

Michael O'Brian
Code Savvy Consultants
Inspector911.com
www.codesavvyconsultants.com
www.inspector911.com
Office: 313-618-6401
Cell: 810-459-0116

On Oct 21, 2009, at 9:38 AM, "Bobby Gillett" <[email protected] 
 > wrote:

> In NFPA 70, somewhere. Every electrical inspector I have had will  
> let us
> enter a room but not exit, with main, branch line, etc. (any  
> piping). I'll
> try to put my finger on it.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of  
> Fletcher, Ron
> Sent: Wednesday, October 21, 2009 8:30 AM
> To: [email protected]
> Subject: RE: Water Filled Pipe in Telecomm Room?
>
> Where does it say "not exit electrical rooms"? I know about the
> restricted space limitations and the required clearances.
>
> Ron Fletcher
> Aero Automatic
> Phoenix
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bobby
> Gillett
> Sent: Wednesday, October 21, 2009 6:25 AM
> To: [email protected]
> Subject: RE: Water Filled Pipe in Telecomm Room?
>
> I think what is flagging you is the fact the electrical code causes us
> to
> enter and not exit electrical rooms and has restrictions on  
> placement of
> pipe. You might check with the electrical inspector, or whoever would
> have
> that jurisdiction ,and see if it applies to the telecomm room as well.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brown,
> Mike
> Sent: Wednesday, October 21, 2009 8:16 AM
> To: [email protected]
> Subject: RE: Water Filled Pipe in Telecomm Room?
>
> Also, I forgot to mention the telecomm room has no ceiling.
>
> Mike Brown
> Project Designer
> Sunland Fire Protection
> 1218 Elon Place
> High Point, NC 27263
> Ph. 336.886.7027 Ext. 140
> Fax: 336.886.7024
> WWW.SUNLANDFIRE.COM
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, October 21, 2009 9:14 AM
> To: [email protected]
> Subject: RE: Water Filled Pipe in Telecomm Room?
>
> Nothing prevents you from running it above the room unless there's  
> some
> military spec saying you can't.  NFPA doesn't prevent it. Are you
> providing a sprinkler in the room?
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brown,
> Mike
> Sent: Wednesday, October 21, 2009 9:10 AM
> To: [email protected]
> Subject: Water Filled Pipe in Telecomm Room?
>
> I working on a design for an existing military barrack... and the  
> FPE is
> directing us to run our main through a telecomm room? I am trying to
> find something saying that I can or can't do this? Any thoughts?  
> Thanks
> in advance.
>
>
>
> Mike Brown
>
> Project Designer
>
> Sunland Fire Protection
>
> 1218 Elon Place
>
> High Point, NC 27263
>
> Ph. 336.886.7027 Ext. 140
>
> Fax: 336.886.7024
>
> WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to