I agree, as I say its general practice now to avoid them, and to only enter
if necessary. We decided to leave that battle alone.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, October 21, 2009 9:06 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

Most of the time it's best to go around just for the simple reason being
that these rooms can get very crowded overhead with cable trays, conduit
banks and the like.  No point fighting for space for a main if you can avoid
it.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Wednesday, October 21, 2009 10:01 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

We sprinkle them all the time, they allow us to enter to protect the room
but not pass through. My experience in various states all had the same
results. Now it's general practice here to go around them with all piping
and only enter to protect the room. Our field men will even all us on it if
we missed it or the room was labeled as storage and came up later to be an
electrical room, because they have had to change it in the past. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, October 21, 2009 8:54 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

There is no wording for such a requirement.  Only exception in the NEC is
for Vaults but if you read the handbook commentary you'll see that sprinkler
piping is exempt from that requirement there as well.

If you read section 110.26(F)1.C of the NEC you you'll get a bunch of
circular wording but the basic intent is spelled out.  The majority of the
electrical inspectors are making things up as they go based on old wives
tales and something someone else did decades ago because he could, not
because it was a code requirement.

Make them show you the text reference.

Electrical equipment rooms, telecom rooms, computer rooms, etc are no
different than any other room in the building when it comes to requiring
sprinklers.  There are some exceptions to the requirement in NFPA 13 with
parallel wording in some building codes but to not sprinkler the room
requires other construction and operation measures to be adhered to in order
to be compliant.

In a lot of commercial and residential bldgs. the electrical room could be
the room where the greatest chance for fire is present.  Yet it is the one
room that is most often left unprotected due to someone's boogie-man fears
of water and electricity. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Wednesday, October 21, 2009 9:38 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

In NFPA 70, somewhere. Every electrical inspector I have had will let us
enter a room but not exit, with main, branch line, etc. (any piping). I'll
try to put my finger on it.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Wednesday, October 21, 2009 8:30 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

Where does it say "not exit electrical rooms"? I know about the restricted
space limitations and the required clearances.

Ron Fletcher
Aero Automatic
Phoenix

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Wednesday, October 21, 2009 6:25 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

I think what is flagging you is the fact the electrical code causes us to
enter and not exit electrical rooms and has restrictions on placement of
pipe. You might check with the electrical inspector, or whoever would have
that jurisdiction ,and see if it applies to the telecomm room as well.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brown, Mike
Sent: Wednesday, October 21, 2009 8:16 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

Also, I forgot to mention the telecomm room has no ceiling.

Mike Brown
Project Designer
Sunland Fire Protection
1218 Elon Place
High Point, NC 27263
Ph. 336.886.7027 Ext. 140
Fax: 336.886.7024
WWW.SUNLANDFIRE.COM


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, October 21, 2009 9:14 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

Nothing prevents you from running it above the room unless there's some
military spec saying you can't.  NFPA doesn't prevent it. Are you providing
a sprinkler in the room?  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brown, Mike
Sent: Wednesday, October 21, 2009 9:10 AM
To: [email protected]
Subject: Water Filled Pipe in Telecomm Room?

I working on a design for an existing military barrack... and the FPE is
directing us to run our main through a telecomm room? I am trying to find
something saying that I can or can't do this? Any thoughts? Thanks in
advance.

 

Mike Brown

Project Designer

Sunland Fire Protection

1218 Elon Place 

High Point, NC 27263

Ph. 336.886.7027 Ext. 140

Fax: 336.886.7024

WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM> 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to