And herein lies where it appears there is some discrepancy.

Where is the term "Sprinkler Protection" defined as you've stated?  Sorry but 
someone has done some extrapolation of the terms.

It would be virtually impossible to prevent water from entering the dedicated 
electrical space unless you placed physical barriers in the way.  Then if you 
did that you'd be creating an obstruction to sprinkler discharge.  There is 
also wording concerning waterproof covers or shields over equipment so spraying 
on top of the equipment is obviously assumed to be a regular occurrence when 
sprinklers are discharging and would hardly require a clarification in the NEC.

Plus if sprinkler piping was not permitted to intrude into the dedicated space, 
why would (c) even mention the word piping, why wouldn't it mention sprinkler 
discharge instead if it meant the water spray from a sprinkler?  



----------------------------------------
QUOTE:
"(c) Sprinkler Protection. Sprinkler protection shall be permitted for the 
dedicated space where the piping complies with this section.  "The NEC is 
specific here and the operative term "Sprinkler Protection" means its ok to 
spray water into the dedicated equipment space, as opposed to saying "sprinkler 
piping" which is not permitted in the dedicated equipment space.
 
Hope this helps,
 
John Drucker Jr CET "
-----------------------------------------


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, October 21, 2009 10:34 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room? 

(c) Sprinkler Protection. Sprinkler protection shall be permitted for the 
dedicated space where the piping complies with this section.  "The NEC is 
specific here and the operative term "Sprinkler Protection" means its ok to 
spray water into the dedicated equipment space, as opposed to saying "sprinkler 
piping" which is not permitted in the dedicated equipment space.
 
Hope this helps,
 
John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 
 



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Wednesday, October 21, 2009 9:38 AM
To: [email protected]
Subject: [SPAM] - RE: Water Filled Pipe in Telecomm Room? - Email has different 
SMTP TO: and MIME TO: fields in the email addresses

In NFPA 70, somewhere. Every electrical inspector I have had will let us enter 
a room but not exit, with main, branch line, etc. (any piping).
I'll try to put my finger on it.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Wednesday, October 21, 2009 8:30 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

Where does it say "not exit electrical rooms"? I know about the restricted 
space limitations and the required clearances.

Ron Fletcher
Aero Automatic
Phoenix

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Wednesday, October 21, 2009 6:25 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

I think what is flagging you is the fact the electrical code causes us to enter 
and not exit electrical rooms and has restrictions on placement of pipe. You 
might check with the electrical inspector, or whoever would have that 
jurisdiction ,and see if it applies to the telecomm room as well.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brown, Mike
Sent: Wednesday, October 21, 2009 8:16 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

Also, I forgot to mention the telecomm room has no ceiling.

Mike Brown
Project Designer
Sunland Fire Protection
1218 Elon Place
High Point, NC 27263
Ph. 336.886.7027 Ext. 140
Fax: 336.886.7024
WWW.SUNLANDFIRE.COM


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, October 21, 2009 9:14 AM
To: [email protected]
Subject: RE: Water Filled Pipe in Telecomm Room?

Nothing prevents you from running it above the room unless there's some 
military spec saying you can't.  NFPA doesn't prevent it. Are you providing a 
sprinkler in the room? 


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brown, Mike
Sent: Wednesday, October 21, 2009 9:10 AM
To: [email protected]
Subject: Water Filled Pipe in Telecomm Room?

I working on a design for an existing military barrack... and the FPE is 
directing us to run our main through a telecomm room? I am trying to find 
something saying that I can or can't do this? Any thoughts? Thanks in advance.



Mike Brown

Project Designer

Sunland Fire Protection

1218 Elon Place

High Point, NC 27263

Ph. 336.886.7027 Ext. 140

Fax: 336.886.7024

WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)



CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to