And herein lies where it appears there is some discrepancy. Where is the term "Sprinkler Protection" defined as you've stated? Sorry but someone has done some extrapolation of the terms.
It would be virtually impossible to prevent water from entering the dedicated electrical space unless you placed physical barriers in the way. Then if you did that you'd be creating an obstruction to sprinkler discharge. There is also wording concerning waterproof covers or shields over equipment so spraying on top of the equipment is obviously assumed to be a regular occurrence when sprinklers are discharging and would hardly require a clarification in the NEC. Plus if sprinkler piping was not permitted to intrude into the dedicated space, why would (c) even mention the word piping, why wouldn't it mention sprinkler discharge instead if it meant the water spray from a sprinkler? ---------------------------------------- QUOTE: "(c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section. "The NEC is specific here and the operative term "Sprinkler Protection" means its ok to spray water into the dedicated equipment space, as opposed to saying "sprinkler piping" which is not permitted in the dedicated equipment space. Hope this helps, John Drucker Jr CET " ----------------------------------------- Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of John Drucker Sent: Wednesday, October 21, 2009 10:34 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? (c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section. "The NEC is specific here and the operative term "Sprinkler Protection" means its ok to spray water into the dedicated equipment space, as opposed to saying "sprinkler piping" which is not permitted in the dedicated equipment space. Hope this helps, John Drucker Jr CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Borough of Red Bank, NJ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Wednesday, October 21, 2009 9:38 AM To: [email protected] Subject: [SPAM] - RE: Water Filled Pipe in Telecomm Room? - Email has different SMTP TO: and MIME TO: fields in the email addresses In NFPA 70, somewhere. Every electrical inspector I have had will let us enter a room but not exit, with main, branch line, etc. (any piping). I'll try to put my finger on it. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Fletcher, Ron Sent: Wednesday, October 21, 2009 8:30 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? Where does it say "not exit electrical rooms"? I know about the restricted space limitations and the required clearances. Ron Fletcher Aero Automatic Phoenix -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Wednesday, October 21, 2009 6:25 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? I think what is flagging you is the fact the electrical code causes us to enter and not exit electrical rooms and has restrictions on placement of pipe. You might check with the electrical inspector, or whoever would have that jurisdiction ,and see if it applies to the telecomm room as well. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brown, Mike Sent: Wednesday, October 21, 2009 8:16 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? Also, I forgot to mention the telecomm room has no ceiling. Mike Brown Project Designer Sunland Fire Protection 1218 Elon Place High Point, NC 27263 Ph. 336.886.7027 Ext. 140 Fax: 336.886.7024 WWW.SUNLANDFIRE.COM -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, October 21, 2009 9:14 AM To: [email protected] Subject: RE: Water Filled Pipe in Telecomm Room? Nothing prevents you from running it above the room unless there's some military spec saying you can't. NFPA doesn't prevent it. Are you providing a sprinkler in the room? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brown, Mike Sent: Wednesday, October 21, 2009 9:10 AM To: [email protected] Subject: Water Filled Pipe in Telecomm Room? I working on a design for an existing military barrack... and the FPE is directing us to run our main through a telecomm room? I am trying to find something saying that I can or can't do this? Any thoughts? Thanks in advance. Mike Brown Project Designer Sunland Fire Protection 1218 Elon Place High Point, NC 27263 Ph. 336.886.7027 Ext. 140 Fax: 336.886.7024 WWW.SUNLANDFIRE.COM <http://WWW.SUNLANDFIRE.COM> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)