I'd ask em where in 13R it says you cannot do the individual risers, 13 or
13R or 13D. Short of a high rise needing zoning by floor (I think, we don't
encounter many) we use them in 13R and d all the time, and also did one in a
13 hotel, 4-story over parking garage with rental spaces on 1st that kicked
it out of 13R (as did the garage but since it was subterranean, there was a
leg to stand on, removed by the rental space not incidental to the
residential nature of a hotel).

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Tuesday, November 10, 2009 11:21 AM
To: [email protected]
Subject: RE: System subdivision

Thanks for all the replies.  I got the same answer back from NFPA that
13 applies to 13 not 13R.
Dewayne 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joe
Burtell
Sent: Tuesday, November 10, 2009 10:04 AM
To: [email protected]
Subject: RE: System subdivision

Remind him this is a 13R system and per NFPA 13R 02'

6.7.2.1 For areas outside the dwelling unit, the following criteria
shall comply with specifications in NFPA 13, Standard for the
Installation of Sprinkler Systems, unless permitted by
6.7.2.2 and 6.7.2.3:
(1) Design discharge
(2) Number of design sprinklers
(3) Sprinkler coverage
(4) Position of sprinklers

These are the only 4 things we fall back to NFPA 13 for. There are a few
other little things like hangers and EQ bracing but system subdivision
is not one of them. We have done the bird cage design for years and no
one has ever said a word.


Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [email protected]
Web Site: http://www.burtellfire.com
P please don't print this e-mail unless you really need to




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Tuesday, November 10, 2009 8:40 AM
To: [email protected]
Subject: RE: System subdivision

Yes this is a 13R birdcage system that the AHJ is telling us that it is
not allowed.  He stated 8.15.21 as his basis for requiring horizontal
piping on each floor.  Since this reference is out of 13 I didn't think
it applied to a 13R system. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cliff
Whitfield
Sent: Tuesday, November 10, 2009 9:03 AM
To: [email protected]
Subject: RE: System subdivision

Dewayne,

I didn't look up the section you mentioned but it sounds like you are
describing a "bird-cage" system.  We used them a lot in 13R in cold
climates to eliminate the need to have any piping in the attic areas
that could be subject to freezing.  You lose the ability to control or
zone the floors but it is sometimes the best approach for the building
owner to keep everything wet and avoid A/F which is more labor intensive
and costly to maintain.

If this is not what you were asking, sorry.

Cliff Whitfield, SET
 
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
 
Phone: 850-526-1886
Fax:   850-526-1884
Cell:   850-557-1886
 
www.fire-design.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Tuesday, November 10, 2009 7:58 AM
To: [email protected]
Subject: System subdivision

A) Can section NFPA 13 (07ed) 8.15.21 be applied to NFPA 13R sprinklered
building?

B)Can a multiple floor building, not a high rise, be supplied with
sprinkler piping with the following arrangement and still comply with
section 8.15.21?

    1st floor supplied by horizontal piping with upper floors supplied
by individual rises to sprinklers from 1st floor horizontal piping?

Thanks,

Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to