I would not approve it based on the fact we have a local code requirement to 
have a 10 psi cushion.  However, without that local code requirement it would 
definitely be approved. Without a local code requirement for a cushion there is 
no basis to not approve it.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mike Hairfield
Sent: Monday, November 30, 2009 12:17
To: AFSA SprinklerFORUM; Richardson, R
Subject: RE: Calcs-How much margin


I would approve it but ask for "As Built" Calcs!!!!!

 

Mike
 
> From: [email protected]
> To: [email protected]
> Date: Mon, 30 Nov 2009 14:15:07 -0600
> Subject: RE: Calcs-How much margin
> 
> I would approve it.
> I would also check the calculations VERY, VERY close.
> 
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
> 
> ** Note new email address: [email protected]
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Monday, November 30, 2009 2:11 PM
> To: [email protected]
> Subject: Calcs-How much margin
> 
> I've got a calc I'm reviewing, after all said and done, 3.63 psi margin 
> between demand and available. Designer used 4.2K heads to get the flow 
> exactly to the decimal of the required flow. This is an industrial type 
> project. With a .15 gpm/sf density at 92 sf per head, the flow would be 13.8 
> gpm and he's dead on the money. The concern would be that over the years if 
> there was any change in the water supply or decay of the piping, that the 
> operation of half the design area would be questionable. 
> 
> Would you approve or reject this design? Is this cutting it just a bit close?
> 
> 
> 
> 
> Craig L. Prahl, CET 
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC 29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to