Travis got it right.  They can not use 4.2 K sprinklers if it OH or
higher.  Reject!!!!

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis
Mack
Sent: Monday, November 30, 2009 3:18 PM
To: [email protected]
Subject: Re: Calcs-How much margin

Without checking, I thought you could only use small orifice sprinklers
in
light hazard?

Ok, I did check.  I think this section says you can only use them in LH:

8.3.4 Small Orifice Sprinklers.
8.3.4.1  For light hazard occupancies not requiring as much water as is
discharged by a sprinkler with a nominal K-factor of K-5.6 (80)
operating
at 7 psi (0.5 bar), sprinklers having a smaller orifice shall be
permitted, subject to the following restrictions:
(1)     The system shall be hydraulically calculated.
(2)     Sprinklers with nominal K-factors of less than K-5.6 (80) shall
be
installed only in wet pipe sprinkler systems or in accordance with the
limitations of 8.3.4.2 or 8.3.4.3.
(3)     A listed strainer shall be provided on the supply side of
sprinklers
with nominal K-factors of less than K-2.8 (40).


> I've got a calc I'm reviewing, after all said and done, 3.63 psi
margin
> between demand and available.  Designer used 4.2K heads to get the
flow
> exactly to the decimal of the required flow.  This is an industrial
type
> project.  With a .15 gpm/sf density at 92 sf per head, the flow would
be
> 13.8 gpm and he's dead on the money.  The concern would be that over
the
> years if there was any change in the water supply or decay of the
piping,
> that the operation of half the design area would be questionable.
>
> Would you approve or reject this design?  Is this cutting it just a
bit
> close?
>
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
>


-- 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to