Well, obviously the bogus flow test and I'll accept Mr Denhardt's comment
without checking- he's WAY smarter than I am.

However- if the flow test was legitimate but they didn't knock off 10% - or
BETTER- adjust for lowest tank gradient in its actual value- data is
generally available from the water company for tank height during the flow
test. If they didn't correct for tank gradient or toss a cushion at it (hey-
where did the 10% come from when throwing in an allowance for tank gradient
and future degradation???) then a <5PSI cushion is pretty slim. However, if
the water is THAT bad, how do you give a 10 PSI cushion on a 35/3...@1500 flow
test that can do the job with a 10% cushion after gradient correction? I
know- with a fire pump.

Cliff, when we go in prior to approvals and we're concerned in the least bit
that we cut something too thin, I look to see where we can readily recover
from it. Like throwing small crossmains on a tree, 2nd feed from a riser to
a grid, etc. 

And Chris is right- it's never too late, just always more expensive than you
didn't figure for.

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Craig Rauch
Sent: Monday, November 30, 2009 3:50 PM
To: [email protected]
Subject: RE: Calcs-How much margin

Please forgive the sidebar. What do you require for the adjustment required
by 23.2.1.2 of NFPA 13 (2007)

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David
Blackwell
Sent: Monday, November 30, 2009 3:37 PM
To: [email protected]
Subject: RE: Calcs-How much margin

As an AHJ we are in a similar position and would have to accept it if it met
the absolute code minimum requirements.  

These are MINIMUM requirements.  Many projects may need to be designed to a
higher level than the legal minimum.  That is why in SC the designer is
required by State Law [See ยง40-10-250(B) at
http://www.scstatehouse.gov/code/t40c010.htm] to be either a PE or [when
exempt under the engineering law] a SC licensed sprinkler contractor with a
NICET IV.

It is the responsibility of the designer to account for reasonably
foreseeable problems with the water supply capacity during the design life
of the system.  The designer will be the person in court being asked to
justify their design choices if the system fails...  The NFPA Handbook
commentary to (2007) NFPA 13 23.1.2 [page 844] provides good information
that should be read and carefully considered by the designer.

 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richardson, R
Sent: Monday, November 30, 2009 3:20 PM
To: [email protected]
Subject: RE: Calcs-How much margin

I would not approve it based on the fact we have a local code requirement to
have a 10 psi cushion.  However, without that local code requirement it
would definitely be approved. Without a local code requirement for a cushion
there is no basis to not approve it.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike
Hairfield
Sent: Monday, November 30, 2009 12:17
To: AFSA SprinklerFORUM; Richardson, R
Subject: RE: Calcs-How much margin


I would approve it but ask for "As Built" Calcs!!!!!

 

Mike
 
> From: [email protected]
> To: [email protected]
> Date: Mon, 30 Nov 2009 14:15:07 -0600
> Subject: RE: Calcs-How much margin
> 
> I would approve it.
> I would also check the calculations VERY, VERY close.
> 
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
> 
> ** Note new email address: [email protected]
> 
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
> Sent: Monday, November 30, 2009 2:11 PM
> To: [email protected]
> Subject: Calcs-How much margin
> 
> I've got a calc I'm reviewing, after all said and done, 3.63 psi margin
between demand and available. Designer used 4.2K heads to get the flow
exactly to the decimal of the required flow. This is an industrial type
project. With a .15 gpm/sf density at 92 sf per head, the flow would be 13.8
gpm and he's dead on the money. The concern would be that over the years if
there was any change in the water supply or decay of the piping, that the
operation of half the design area would be questionable. 
> 
> Would you approve or reject this design? Is this cutting it just a bit
close?
> 
> 
> 
> 
> Craig L. Prahl, CET 
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC 29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to