I know John I'm just waiting for the "UBER" density curves for Storage with
"Specific Application Storage" Heads, you know when they're no longer
specific application, but the "storage standard heads". You know they start
@ 0.30 and go up to Oh lets allow some room for growth so let's say 2.00
GPM/SF.

I just started down this road a question Craig had an OH occupancy that was
done with 4.2K heads, it didn't say storage or not. Just 4.2K. Then Ron was
talking about TYCO Literature or Listing appeared to allow 4.2K in OH, so I
was making a point that for some OH applications 5.6K heads that are OH
listed are not allowed. And Now we're here!



Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Denhardt
Sent: Tuesday, December 01, 2009 11:32 AM
To: [email protected]
Subject: RE: Calcs-How much margin

It has been like that for the last couple of cycles.  Storage is only
considered OH or EH if you are sent back to the occupancy chapters.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Tuesday, December 01, 2009 1:41 PM
To: [email protected]
Subject: RE: Calcs-How much margin

So are you saying storage is not OH? (I know not all storage is necessarily
OH) 

Are we creating a new category? LH, OHI, OHII, EXI EHII and Storage? 

Not that I think that's a bad idea.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Tuesday, December 01, 2009 11:13 AM
To: [email protected]
Subject: Re: Calcs-How much margin

that's a restriction that applies only to STORAGE

Roland

On Dec 1, 2009, at 8:38 AM, Thom McMahon wrote:

> NFPA 13 has other restrictions on orifice size in OH occupancies, and 
> even 5.6K heads that are listed for OH cannot be used for design 
> densities over 0.30 GPM/SF (From memory, could be wrong #)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to