Slight correction -they will be differentiating between suppression  
and control mode but not by name of the sprinkler (they will all be  
STORAGE sprinklers).  There will be criteria for control (under the  
CMSA rules) and suppression (under the ESFR rules).  The sprinkler  
types will be differentiated by the thermal sensitivity (1 of 5  
characteristics that will part of their approval / listing (per 13  
definition).

Roland

On Dec 1, 2009, at 11:31 AM, George Church wrote:

> Or just qualify your proposal that storage can't exceed 12' and go  
> OH 2 with
> EC heads in that 40' tall box.....
>
> In April 2010 FM Global is going to slim down the selection of heads  
> to:
> Storage
> Non-storage
> Residential
> Special
> They won't be differentiating between suppression and control modes,  
> and
> several other quantum changes in an effort to simplify design  
> criteria.