Craig,

Without spending time to dig thru 13, I believe that is correct.

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Thursday, December 03, 2009 6:15 AM
To: [email protected]
Subject: Preaction area increase

Need clarification:

Based on NFPA 13, 11.2.3.2.5 only DIPA systems require the 30% area
increase.  This does not apply to Single or Non-interlocked PA systems.


NFPA 13, 2007, 12.5.1 area increase of 30% only applies to preaction systems
installed in storage areas.

Correct? 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 