Yes. That is a valid concern. We offset that here by requiring the operation 
temp of the vents to be significantly higher than the ESFR temp ratings.

Steve

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Thursday, December 17, 2009 7:30 AM
To: '[email protected]'
Subject: RE: ESFR DOES WHAT???

My understanding is that smoke vents impair the function of esfr systems by 
drafting heat away from the fire area and setting off sprinklers that don't 
help with suppression.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, December 17, 2009 8:21 AM
To: [email protected]
Subject: RE: ESFR DOES WHAT???

We got a similar response where the vents were used for the increased distance. 
 The Underwriter required the vents to be either manual or have links at a 
higher temp rating than the sprinklers and the AHJ concurred.  Vents had to go 
in.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Thursday, December 17, 2009 9:10 AM
To: [email protected]
Subject: RE: ESFR DOES WHAT???

I think some time ago we asked for an interpretation from ICC and were told 
that vents are required with ESFR's if the egress distance exception is taken. 
If I can find a record of the emails I'll let you know. It may also have been a 
topic on the ICC Forum.

Ron Fletcher
Aero Automatic
Phoenix, AZ


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, December 17, 2009 7:04 AM
To: [email protected]
Subject: RE: ESFR DOES WHAT???

Vince, we did a job last year where our variance was approved and here's the 
logic train:

Egress distance can be increased past 250' if heat and smoke vents are 
provided. 
So we "pencil vents in". 
Then we provide an ESFR system so the vents aren't required, erase them.
Extended egress distance in section labeled Extended egress distance with heat 
and smoke Vents was basis for the increase granted, but none of them were 
installed.

The architect chairing the variance committee voted for us, the other two guys 
split, it carried.

Yes, you can omit H&S vents with ESFR but I'd read the fine print and if you 
need to, as the top example illustrates, about anything is possible with 
linguistics.

glc


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Thursday, December 17, 2009 8:48 AM
To: [email protected]
Subject: ESFR DOES WHAT???

Good morning, forum --

I want to use control mode heads in an existing warehouse building under 30 ft 
in height.

Somebody (working for the owner) says that he would prefer ESFR heads because 
(his thought) it eliminates the requirement for heat and smoke vents.

If that's true, I would have thought that the sprinkler manufacturer's 
marketing people would have jumped all over this.

That aside, has anybody else ever run into anything like this?

                                                               thanks! 
Merry Christmas!

                                                              Vince

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to