I learned an interesting phrase from a former staff liason at NFPA; during
committee meetings he'd observe:
"Since I'm not on the committee, I'm not entitled to an opinion. But if I
were, I'd ......" 

Nice caveat, he could participate without participating. And as a PE, he
would otherwise BE entitled to an opinion, but not in that liason role.

I've used the same language repeatedly, good thing he didn't ask for
residuals. 
My mantra is:
"I'm not a PE, so I'm not entitled to an opinion. But if I were, I'd ......"

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Thursday, December 17, 2009 11:29 AM
To: [email protected]
Subject: RE: ESFR DOES WHAT???

No the consensus was if not for exiting exceptions vents are not required by
the IFC.  

Assuming the IFC is adopted without amendment as LAW the LAW allows this
omission.  The only further exception is if the AHJ has changed the LAW and
is legally allowed to change the LAW.  For example in MN local officials
cannot change the State LAW. If it's a policy to still require vents with
ESFR it isn't worth the paper it's written on.  Only the legislative branch
can change the LAW.  This might be a city council passing an ordinance again
if legally allowed.  Again for example in MN a city council cannot pass an
ordinance changing the State LAW.   The AHJ opinion is irrelevant.  

Also be careful about advising the owner on issues such as this.  It treads
on licensing as PE work.  You can certainly hand him a code book open to the
page of interest but as soon as you tell him he doesn't need something like
vents you have probably crossed the line (unless you are licensed).  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Thursday, December 17, 2009 9:59 AM
To: [email protected]
Subject: ESFR DOES WHAT???

--- So the consensus of opinion is that requirement of smoke and heat 
vents will or
will not be required depending  on the AHJ and whether or not he buys into
IFC.

Kinda what I thought... hope I don't get the guy that held up a plan 
approval because
we didn't put heads under a couple of doors... we did show plugs for 
that if he wanted them.

Thanks for your help, guys!

                                                                    Vince

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to