The 13 handbook commentary for 14.4.4.5 (2002) 
does not include any decrease for copper and I 
have never used one. 2010 has similar language. 
The FP handbook does not address it. My 
questioning is on the degradation of copper pipe 
and decrease in C Factor because of it. Never 
heard of it before. This water department person 
tends to pull things out of his Botox, but I want 
to be sure before I challenge him.


At 06:28 PM 12/17/2009, you wrote:
>My reference manual lists the range for copper 
>as 150-120. So I would say it is within reason.
>
>Matt Grisé PE*, LEED AP
>Sales Engineer
>Alliance Fire Protection
>*Licensed in KS & MO
>
>913.888.0647 ph
>913.888.0618 f
>913.927.0222 cell
>www. AFPsprink.com
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Thursday, December 17, 2009 5:08 PM
>To: [email protected]
>Subject: C factor in old copper pipe
>
>I am working on a 13D system which is fed by a copper pipe from the
>public supply. I have been asked by the water company (who has review
>authority in this situation) to decrease the C factor for the copper
>pipe from 150 to 120 due to age. I have done this several times in
>steel and CI pipe, but never in copper. Is this appropriate?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to