Todd, is it possible to run a flow test at the end of the copper line to
simply measure the real thing instead of degrading it?

We'd had an AHJ want to degrade DI UG down to C=80 or 90, until we removed a
section and showed it to him- clean as a whistle, allowed C=140 after all.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, December 21, 2009 7:16 AM
To: [email protected]
Subject: RE: C factor in old copper pipe

I have no problem with C120 for the pipe from a 
technical standpoint, but it does make the calcs 
go over the curve. (2/3 of the system friction 
loss is in the underground). I have no idea how 
old the pipe is and there is no cathodic 
protection that I am aware of. As far as where 
they came up with the adjustment, see my Botox comment in the previous post.



At 08:39 AM 12/18/2009, you wrote:
>The book I looked in was a Mechanical 
>Engineering Reference Manual. It has a wider 
>range of materials listed than 13, so I checked 
>there. I don't know that 13 requires any 
>downgrade for copper - I don't really run into 
>copper sprinkler pipe all that often. The only 
>thing that I could say is that from a standpoint 
>of the actual performance of the pipe, it is 
>possible that it could have aged to a point 
>where its c-value is 120. Out of curiosity: how 
>old is the pipe? Also, how did the water company 
>come up with the adjustment? Do they have 
>cathodic protection of their underground copper lines?
>
>Does the change have a major effect on your calcs?
>
>Matt Grisé PE*, LEED AP
>Sales Engineer
>Alliance Fire Protection
>*Licensed in KS & MO
>
>913.888.0647 ph
>913.888.0618 f
>913.927.0222 cell
>www. AFPsprink.com
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Todd
Williams
>Sent: Thursday, December 17, 2009 5:59 PM
>To: [email protected]
>Subject: RE: C factor in old copper pipe
>
>The 13 handbook commentary for 14.4.4.5 (2002)
>does not include any decrease for copper and I
>have never used one. 2010 has similar language.
>The FP handbook does not address it. My
>questioning is on the degradation of copper pipe
>and decrease in C Factor because of it. Never
>heard of it before. This water department person
>tends to pull things out of his Botox, but I want
>to be sure before I challenge him.
>
>
>At 06:28 PM 12/17/2009, you wrote:
> >My reference manual lists the range for copper
> >as 150-120. So I would say it is within reason.
> >
> >Matt Grisé PE*, LEED AP
> >Sales Engineer
> >Alliance Fire Protection
> >*Licensed in KS & MO
> >
> >913.888.0647 ph
> >913.888.0618 f
> >913.927.0222 cell
> >www. AFPsprink.com
> >
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Todd
Williams
> >Sent: Thursday, December 17, 2009 5:08 PM
> >To: [email protected]
> >Subject: C factor in old copper pipe
> >
> >I am working on a 13D system which is fed by a copper pipe from the
> >public supply. I have been asked by the water company (who has review
> >authority in this situation) to decrease the C factor for the copper
> >pipe from 150 to 120 due to age. I have done this several times in
> >steel and CI pipe, but never in copper. Is this appropriate?
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, Connecticut
> >www.fpdc.com
> >860.535.2080
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to