There is no practical way to run a flow test on 
the copper. This is one of several issues at this 
site including a significant drop in residual 
pressures in the building. My guess is that the 
final solution will be to replace the main. Given 
that we had 16-18" of snow this weekend, nobody 
is going to like that (although it is supposed to be in the 50s on Saturday)



At 07:39 AM 12/21/2009, you wrote:
>Todd, is it possible to run a flow test at the end of the copper line to
>simply measure the real thing instead of degrading it?
>
>We'd had an AHJ want to degrade DI UG down to C=80 or 90, until we removed a
>section and showed it to him- clean as a whistle, allowed C=140 after all.
>
>glc
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Monday, December 21, 2009 7:16 AM
>To: [email protected]
>Subject: RE: C factor in old copper pipe
>
>I have no problem with C120 for the pipe from a
>technical standpoint, but it does make the calcs
>go over the curve. (2/3 of the system friction
>loss is in the underground). I have no idea how
>old the pipe is and there is no cathodic
>protection that I am aware of. As far as where
>they came up with the adjustment, see my Botox comment in the previous post.
>
>
>
>At 08:39 AM 12/18/2009, you wrote:
> >The book I looked in was a Mechanical
> >Engineering Reference Manual. It has a wider
> >range of materials listed than 13, so I checked
> >there. I don't know that 13 requires any
> >downgrade for copper - I don't really run into
> >copper sprinkler pipe all that often. The only
> >thing that I could say is that from a standpoint
> >of the actual performance of the pipe, it is
> >possible that it could have aged to a point
> >where its c-value is 120. Out of curiosity: how
> >old is the pipe? Also, how did the water company
> >come up with the adjustment? Do they have
> >cathodic protection of their underground copper lines?
> >
> >Does the change have a major effect on your calcs?
> >
> >Matt Grisé PE*, LEED AP
> >Sales Engineer
> >Alliance Fire Protection
> >*Licensed in KS & MO
> >
> >913.888.0647 ph
> >913.888.0618 f
> >913.927.0222 cell
> >www. AFPsprink.com
> >
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Todd
>Williams
> >Sent: Thursday, December 17, 2009 5:59 PM
> >To: [email protected]
> >Subject: RE: C factor in old copper pipe
> >
> >The 13 handbook commentary for 14.4.4.5 (2002)
> >does not include any decrease for copper and I
> >have never used one. 2010 has similar language.
> >The FP handbook does not address it. My
> >questioning is on the degradation of copper pipe
> >and decrease in C Factor because of it. Never
> >heard of it before. This water department person
> >tends to pull things out of his Botox, but I want
> >to be sure before I challenge him.
> >
> >
> >At 06:28 PM 12/17/2009, you wrote:
> > >My reference manual lists the range for copper
> > >as 150-120. So I would say it is within reason.
> > >
> > >Matt Grisé PE*, LEED AP
> > >Sales Engineer
> > >Alliance Fire Protection
> > >*Licensed in KS & MO
> > >
> > >913.888.0647 ph
> > >913.888.0618 f
> > >913.927.0222 cell
> > >www. AFPsprink.com
> > >
> > >
> > >-----Original Message-----
> > >From: [email protected]
> > >[mailto:[email protected]] On Behalf Of Todd
>Williams
> > >Sent: Thursday, December 17, 2009 5:08 PM
> > >To: [email protected]
> > >Subject: C factor in old copper pipe
> > >
> > >I am working on a 13D system which is fed by a copper pipe from the
> > >public supply. I have been asked by the water company (who has review
> > >authority in this situation) to decrease the C factor for the copper
> > >pipe from 150 to 120 due to age. I have done this several times in
> > >steel and CI pipe, but never in copper. Is this appropriate?
> > >
> > >Todd G. Williams, PE
> > >Fire Protection Design/Consulting
> > >Stonington, Connecticut
> > >www.fpdc.com
> > >860.535.2080
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email to:[email protected]
> > >(Put the word unsubscribe in the subject field)
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email to:[email protected]
> > >(Put the word unsubscribe in the subject field)
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, Connecticut
> >www.fpdc.com
> >860.535.2080
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to