Steve,

I have used the KY-Pipe Surge program to conduct surge pressure transit 
analysis for a large loss in order to defend the sprinkler contractor in US 
Federal Court. This is the only surge program that has had significant peer 
review and realistically models the pressure wave effects including the 
additional pressure that results from the pressure wave crossing itself. It can 
also model pressure surge chambers to determine the effects that a curge 
chamber has on the system. If you are using the KY Pipe hydraulic program it is 
easy to import, however it is not a problem with building a model from scratch. 
Read the software manual because you will need to know opening times for check 
valves, OS&Y valves and all related valves. 

Regards

Jim Davidson, PE 

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Kowkabany
Sent: Friday, January 01, 2010 6:01 PM
To: [email protected]
Subject: Surge Calculations

Has anyone ever had to perform a surge analysis to determine the
water-hammer forces on piping for the purpose of designing pipe restraints
for a fire protection system supplied by a pump.  We are being asked to
provide this and the software KY Pipe was recommended.  I'm used to just
using NFPA 24 for this.  It's a big underground system at an overseas
manufacturing facility.

 

Any insights or recommendations on modeling software would be greatly
appreciated.

 

Thanks and Happy New Years!

 

 

Steve Kowkabany, P.E.

Fire Protection Engineer

Neptune Fire Protection Engineering LLC

60 Ocean Boulevard, Suite 15

Atlantic Beach, FL 32233

904-652-4200 Phone

904-212-0868 Fax 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to