Steve,

KY - Pipe Surge software is used by many chemical process plants, water 
authorities, pipeline transmission utilities, process engineering firms almost 
all industries conduct surge analysis for their piping systems with the 
exception of the sprinkler industry. It appears that it is not addressed in the 
NFPA code. In the court case the building owner tried to place all of the blame 
onto the sprinkler contractor because the owners design professionals did not 
address the issue.

Regards

JIm 

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Kowkabany
Sent: Monday, January 04, 2010 2:30 PM
To: [email protected]
Subject: RE: Surge Calculations

Thanks Jim and Scot,

KY pipe is actually what we are going to use.  I am learning it now and we
have a couple of experienced users to help me through the process.  It's
good to hear that it's reliable software.  You always wonder how much
validation has been done with physical testing for modeling programs like
this.  It seems like KY Pipe is the industry standard.

Thanks again and have a great week,


Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
60 Ocean Boulevard, Suite 15
Atlantic Beach, FL 32233
904-652-4200 Phone
904-212-0868 Fax 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Monday, January 04, 2010 1:35 PM
To: [email protected]
Subject: RE: Surge Calculations

Steve,

I have used the KY-Pipe Surge program to conduct surge pressure transit
analysis for a large loss in order to defend the sprinkler contractor in US
Federal Court. This is the only surge program that has had significant peer
review and realistically models the pressure wave effects including the
additional pressure that results from the pressure wave crossing itself. It
can also model pressure surge chambers to determine the effects that a curge
chamber has on the system. If you are using the KY Pipe hydraulic program it
is easy to import, however it is not a problem with building a model from
scratch. Read the software manual because you will need to know opening
times for check valves, OS&Y valves and all related valves. 

Regards

Jim Davidson, PE 

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Kowkabany
Sent: Friday, January 01, 2010 6:01 PM
To: [email protected]
Subject: Surge Calculations

Has anyone ever had to perform a surge analysis to determine the
water-hammer forces on piping for the purpose of designing pipe restraints
for a fire protection system supplied by a pump.  We are being asked to
provide this and the software KY Pipe was recommended.  I'm used to just
using NFPA 24 for this.  It's a big underground system at an overseas
manufacturing facility.

 

Any insights or recommendations on modeling software would be greatly
appreciated.

 

Thanks and Happy New Years!

 

 

Steve Kowkabany, P.E.

Fire Protection Engineer

Neptune Fire Protection Engineering LLC

60 Ocean Boulevard, Suite 15

Atlantic Beach, FL 32233

904-652-4200 Phone

904-212-0868 Fax 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 8.5.432 / Virus Database: 270.14.123/2594 - Release Date: 01/04/10
08:24:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to