I am looking for some guidance on the water supply assumptions to consider when designing sprinkler system for a FEMA Trailer. I have seen designs ranging from 100 psi to 20 psi. The water supplies for these units are unknown and it is my view that the design basis should be based upon the low end of what can be expected as these units are connected to the temporary water supply. Generally FEMA is the AHJ and is on site and provides no guidance on what can be expected from the water supply that is hooked up to these units.
I am concerned that we may see systems that won’t work because the supply will fall short of the design basis used. The data plate states the minimum pressure required for the system design as required in 6.4 6.4 Manufactured Home Water Supply. For sprinklered buildings manufactured off-site, the minimum pressure needed to satisfy the system design criteria on the system side of the meter shall be specified on a data plate by the manufacturer. However, what is reasonable? Mike Cabral _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)