Bruce,

Maybe you could give us all a list as to what is essential to you as a
plane reviewer. Todd, Can't you do it faster than "over the weekend?"
}:-)

On Wed, Jan 27, 2010 at 10:14 AM,  <[email protected]> wrote:
>
> Bill,
>
> If a second person is going to review the plans design criteria documentation 
> is crucial. Most projects have a time element. Without this portion of a 
> submittal plan review doesn't start. Why look at pipe hangers or bracing if 
> the design criteria hasn't been affirmed?
>
> Plan reviewers review plans - they don't reverse engineer.
>
> I would also guess that occasionally the designer finds some error during the 
> process of writing down the criteria, and self-corrects.
>
> Structural engineers don't just show how big a beam they are going to use, 
> and what kind of connections. They show the calculations used to show that in 
> accordance with generally accepted stardards, the beam and connections are 
> adequate.
>
>
>
> Yours,
>
> Bruce Verhei
>
> ----- Original Message -----
> From: "Bill Brooks" <[email protected]>
> To: [email protected]
> Sent: Wednesday, January 27, 2010 5:12:57 AM GMT -08:00 US/Canada Pacific
> Subject: How the Heck Did You Come Up With 0.58 over 2000?
>
> Wouldn't it be nice if sprinkler shop drawings for storage occupancies 
> included a table or other method to show the derivation of the design 
> density/area of coverage/head selection etc. As a suggestion, a table with 
> the following data:
>
> Storage arrangement - Racks (single row, etc), shelf, bin box, solid pile, etc
> Rack height -
> Storage height -
> Shelf type -
> Aisle width -
> Commodity class -
> In-rack sprinklers -
> NFPA 13 table -
> NFPA 13 curve -
> Correction for height -
>
> In other words, show the steps used by the designer to get to the selected 
> design parameters.
>
> Bill Brooks
>
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
> 372 Wilett Drive
> Severna Park, MD 21146-1904
> 410-544-3620
> 410-544-3032 FAX
> 412-400-6528 Cell
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to