Oops, meant '07

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Damien
Shannon
Sent: Wednesday, January 27, 2010 3:50 PM
To: [email protected]
Subject: RE: dry system drains

Section 8.16.2.5.3.1 of 2010 states 'Aux drains located in areas subject to
freezing shall be readily accessible'. Would therefore seem ok to be located
in an area prone to freezing so long as the valve is accessible. Would be
difficult to provide a drain in a heated area if you have a dry rack system.

Damien Shannon.
QED Sprinkler Design, Inc.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest Wilson
Sent: Wednesday, January 27, 2010 3:38 PM
To: [email protected]
Subject: RE: dry system drains

7.4.4 applies to Subdivision of systems with check valves.
7.4 is for combined dry pipe and pre-action systems.
7.4.4.4 does not apply to dry systems.
Right? (or am I wrong?)

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Letterman,
Todd
Sent: Wednesday, January 27, 2010 4:17 PM
To: [email protected]
Subject: RE: dry system drains

NFPA 13 2002   7.4.4.4  Section drain lines and dry pipe system
auxiliary drains shall be located in heated areas or inside heated
cabinets to enclose drain valves and auxiliary drains for each section.
I don't know if this is what you are looking for or not. Hope it helps.

Todd Letterman
Fire Protection Engineer
Riverside County Fire Department
(951) 955-5273-Fax(951) 955-4886
[email protected]
 
 
"Life's not about waiting for the storms to pass...
It's about learning to dance in the rain."

-----Original Message-----
From: Robert Thompson [mailto:[email protected]] 
Sent: Tuesday, January 26, 2010 12:25 PM
To: [email protected]
Subject: dry system drains

Is there a code in 13 that states a dry pipe aux. drain or drum drip
need to be in a heated area?
 

Thank you 
 Robert  Thompson 

 DAKOTA 
FIRE PROTECTION 
1710 N. Washington Street 
Grand Forks ND 58206-5327 
Phone # (701) 772-8820 
Fax # (701) 772-7932 
Email [email protected] 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

__________ Information from ESET Smart Security, version of virus signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com


 

__________ Information from ESET Smart Security, version of virus signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 
 

__________ Information from ESET Smart Security, version of virus signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

__________ Information from ESET Smart Security, version of virus signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com


 

__________ Information from ESET Smart Security, version of virus signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 
 

__________ Information from ESET Smart Security, version of virus signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to