I don't see anything in '07 that gives conditions for the aux drain to be
located in a heated area (other than for Wharfs/piers).

I'm not sure if there would be a difference in the types of buildings. Would
seem both have the dry valve located in a heated area, air compressor would
often be located in a 'riser room' and pipe in a colder environment. Both
dealing with drops in pipe (drop downs to feed racks in the storage building
versus drop under obstructions for the Retail examples). Would both not be
equally prone to the warmer air that the compressor is getting from the
riser room, creating condensation and then turning to ice? I could see the
problem with trying to open a closed valve:)

Damien Shannon.
QED Sprinkler Design, Inc.




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Letterman,
Todd
Sent: Thursday, January 28, 2010 10:08 AM
To: [email protected]
Subject: RE: dry system drains

Actually both of you are right about the sections, and yes in a cold
storage facility sometimes it would be difficult to pipe a drip drum or
auxiliary valve to heated area. The only problem is the transition
between differential temperatures with the line. Usually unless there is
something wrong with the Dry system main pitch back to the valve all the
piping with in the cold storage would be the same temp. No condensation
for the drip drum to collect, but in the case of big box retailers who
cover the canopies, garden centers and lumber canopies where the main
and lines sometimes cannot be physically pitched back towards the valve,
the temperature difference between where the valve sits (heated space)
and where the drip drum is placed (outside)(Midwest) is great. You
cannot drain a frozen valve without heat! I think this has been
addressed for many years through proposals but difficult to do depending
on the building. Sorry kind of a winded reply, but I have seen literally
hundreds of these around the country when I traveled, not a whole lot
you can do to drain a drip drum when it is 10 below out side.
 I wished I had the 2010 NFPA 13, but no budget. Let me know if you find
anything else regarding the issue.      

Todd Letterman
Fire Protection Engineer
Riverside County Fire Department
(951) 955-5273-Fax(951) 955-4886
[email protected]
 
 
"Life's not about waiting for the storms to pass...
It's about learning to dance in the rain."

-----Original Message-----
From: Damien Shannon [mailto:[email protected]] 
Sent: Wednesday, January 27, 2010 1:50 PM
To: [email protected]
Subject: RE: dry system drains

Section 8.16.2.5.3.1 of 2010 states 'Aux drains located in areas subject
to
freezing shall be readily accessible'. Would therefore seem ok to be
located
in an area prone to freezing so long as the valve is accessible. Would
be
difficult to provide a drain in a heated area if you have a dry rack
system.

Damien Shannon.
QED Sprinkler Design, Inc.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest
Wilson
Sent: Wednesday, January 27, 2010 3:38 PM
To: [email protected]
Subject: RE: dry system drains

7.4.4 applies to Subdivision of systems with check valves.
7.4 is for combined dry pipe and pre-action systems.
7.4.4.4 does not apply to dry systems.
Right? (or am I wrong?)

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Letterman,
Todd
Sent: Wednesday, January 27, 2010 4:17 PM
To: [email protected]
Subject: RE: dry system drains

NFPA 13 2002   7.4.4.4  Section drain lines and dry pipe system
auxiliary drains shall be located in heated areas or inside heated
cabinets to enclose drain valves and auxiliary drains for each section.
I don't know if this is what you are looking for or not. Hope it helps.

Todd Letterman
Fire Protection Engineer
Riverside County Fire Department
(951) 955-5273-Fax(951) 955-4886
[email protected]
 
 
"Life's not about waiting for the storms to pass...
It's about learning to dance in the rain."

-----Original Message-----
From: Robert Thompson [mailto:[email protected]] 
Sent: Tuesday, January 26, 2010 12:25 PM
To: [email protected]
Subject: dry system drains

Is there a code in 13 that states a dry pipe aux. drain or drum drip
need to be in a heated area?
 

Thank you 
 Robert  Thompson 

 DAKOTA 
FIRE PROTECTION 
1710 N. Washington Street 
Grand Forks ND 58206-5327 
Phone # (701) 772-8820 
Fax # (701) 772-7932 
Email [email protected] 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

__________ Information from ESET Smart Security, version of virus
signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com


 

__________ Information from ESET Smart Security, version of virus
signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 
 

__________ Information from ESET Smart Security, version of virus
signature
database 4811 (20100127) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

__________ Information from ESET Smart Security, version of virus signature
database 4814 (20100128) __________

The message was checked by ESET Smart Security.

http://www.eset.com


 

__________ Information from ESET Smart Security, version of virus signature
database 4815 (20100128) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to