Depends on what he question is. Yes to removing or deleting heads directly over kilns and furnaces. No to blowing the roof off.
On Tue, Feb 2, 2010 at 8:56 PM, Jay Jay Blocker <[email protected]> wrote: > After some research as to why all the uprights were removed from the > branchlines over the top of gas fired kilns I was told the insurance company > told the customer they could be removed. The justification was that if the > heads went off the steam would blow the roof off the building. Has anyone > ever heard of this before? No records of anything with the AHJ's office to > assist. > > J. Blocker > EFPS > (303) 353-9712 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)