If it's a library, unless portions of the system are inappropriately exposed to sub-40 deg. temps, there isn't a code requirement that a library be protected by a particular KIND of system, just that it be per the referenced standard (13). Which gives the designer a choice, that was likely exercised to mitigate the chance of a false discharge irreparably damaging books, archival collections, etc. And likely specified that way. I doubt you'll find a code violation, but the first cost of preaction was undertaken for a reason, so it's the library's decision to put it back into preaction service or not.
Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ford, Charles Sent: Friday, February 12, 2010 7:55 AM To: [email protected] Subject: RE: Impaired preaction We have a customer whose pre-action system for a library is impaired due to electrical/ detection problems. He has had a contractor trip it into a wet pipe system. We are looking for a code reference prohibiting this kind of "repair". Is this possibly just an AHJ decision? Any suggestions? C. Burton Ford Designer- NICET Certified: Fire Alarm, Special Hazards, Sprinkler Design &Sprinkler Inspections NFPA CFPS Cintas Fire Protection-D-47 Warminster, PA 18974 Phone 267-487-1000 Fax 267-487-1010 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Richardson, R Sent: Friday, February 12, 2010 10:37 AM To: [email protected] Subject: RE: Flexible Pipe The engineer quite likely means the use of high pressure steel braided rubber hose, or something similar. We have approved high pressure steel braided rubber hose for these situations often, as long as they installation is such that the hose remain submerged. Not a whole lot of better options that we are aware of at this point. Rich Richardson Seattle Fire Department > > Yeah you read this right. > > I'm reviewing a pacakge and the EOR has called out for flexible pipe at a > couple of areas where he thinks they can't use hard pipe to make the bends, > plus he is wanting some allowance for movement. This is on a pier. > > So I've hunted even though in all my years dabbling in this I can't recall > such an animal. Flexible connections and flexible drops are one thing but a > 10-20 ft section of "flexible" pipe? > > Anyone ever heard or seen such a thing? > > He's not called out any manufacturer and is out of town right now so I can't > ask what he had in mind. > > It's not a sprinkler system, it's a 4" manual, dry standpipe line along the > pier. > > > CH2MHILL/SPB > Craig Prahl > 864-599-4102 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman, CET, FPE Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4861 (20100212) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4861 (20100212) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)