I think it stays tripped by itself. There is no panel, 110 vac solenoid. That's 
part of the electrical
problem. Not supervised, no power and no money to fix properly.

C. Burton Ford
Designer- NICET Certified: Fire Alarm, 
Special Hazards, Sprinkler Design 
&Sprinkler Inspections
NFPA CFPS
Cintas Fire Protection-D-47
Warminster, PA 18974
Phone 267-487-1000
Fax 267-487-1010

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On
Behalf Of Mike Henke
Sent: Friday, February 12, 2010 5:10 PM
To: [email protected]
Subject: RE: Impaired preaction

How is he keeping the preaction valve tripped?
Is the panel in alarm with the solenoid energized?
The solenoid and/or panel may not be able to handle continuous
energization/alarm.
Also what if someone resets the panel?

Regards,

Mike Henke
Potter Electric

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Friday, February 12, 2010 10:58 AM
To: [email protected]
Subject: RE: Impaired preaction

Yup=-
And just plug it with a mech tee when repairs to the detection system
are
completed.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Vining
Sent: Friday, February 12, 2010 11:27 AM
To: [email protected]
Subject: Re: Impaired preaction

How will they get an alarm if a sprinkler operates.  They could install
a
waterflow indicator, but it would have to be removed if they ever use
the
preaction valve again.

Ed Vining

On Fri, Feb 12, 2010 at 8:01 AM, Steve Leyton
<[email protected]>wrote:

> If it's a library, unless portions of the system are inappropriately
> exposed to sub-40 deg. temps, there isn't a code requirement that a
> library be protected by a particular KIND of system, just that it be
per
> the referenced standard (13).    Which gives the designer a choice,
that
> was likely exercised to mitigate the chance of a false discharge
> irreparably damaging books, archival collections, etc.   And likely
> specified that way.   I doubt you'll find a code violation, but the
> first cost of preaction was undertaken for a reason, so it's the
> library's decision to put it back into preaction service or not.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ford,
> Charles
> Sent: Friday, February 12, 2010 7:55 AM
> To: [email protected]
> Subject: RE: Impaired preaction
>
> We have a customer whose pre-action system for a library is impaired
due
> to electrical/ detection
> problems. He has had a contractor trip it into a wet pipe system. We
are
> looking for a code reference
> prohibiting this kind of "repair". Is this possibly just an AHJ
> decision?
> Any suggestions?
>
> C. Burton Ford
> Designer- NICET Certified: Fire Alarm,
> Special Hazards, Sprinkler Design
> &Sprinkler Inspections
> NFPA CFPS
> Cintas Fire Protection-D-47
> Warminster, PA 18974
> Phone 267-487-1000
> Fax 267-487-1010
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On
> Behalf Of Richardson, R
> Sent: Friday, February 12, 2010 10:37 AM
> To: [email protected]
> Subject: RE: Flexible Pipe
>
> The engineer quite likely means the use of high pressure steel braided
> rubber hose, or something
> similar.
>
> We have approved high pressure steel braided rubber hose for these
> situations often, as long as they
> installation is such that the hose remain submerged.  Not a whole lot
of
> better options that we are
> aware of at this point.
>
> Rich Richardson
> Seattle Fire Department
>
> >
> > Yeah you read this right.
> >
> > I'm reviewing a pacakge and the EOR has called out for flexible pipe
> at a
> > couple of areas where he thinks they can't use hard pipe to make the
> bends,
> > plus he is wanting some allowance for movement.  This is on a pier.
> >
> > So I've hunted even though in all my years dabbling in this I can't
> recall
> > such an animal.  Flexible connections and flexible drops are one
thing
> but a
> > 10-20 ft section of "flexible" pipe?
> >
> > Anyone ever heard or seen such a thing?
> >
> > He's not called out any manufacturer and is out of town right now so
I
> can't
> > ask what he had in mind.
> >
> > It's not a sprinkler system,  it's a 4" manual, dry standpipe line
> along the
> > pier.
> >
> >
> > CH2MHILL/SPB
> > Craig Prahl
> > 864-599-4102
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to:
[email protected]
> >
> > To Unsubscribe, send an email
>
to:[email protected]<to%3ASprinklerforum-request@
fire
sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to:
[email protected]
> >
> > To Unsubscribe, send an email
>
to:[email protected]<to%3ASprinklerforum-request@
fire
sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman, CET, FPE
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
>
to:[email protected]<to%3ASprinklerforum-request@
fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
>
to:[email protected]<to%3ASprinklerforum-request@
fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
>
to:[email protected]<to%3ASprinklerforum-request@
fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
>
>
> This e-mail transmission contains information that is intended to be
> confidential and privileged.  If you receive this e-mail and you are
not
> a named addressee you are hereby notified that you are not authorized
to
> read, print, retain, copy or disseminate this communication without
the
> consent of the sender and that doing so is prohibited and may be
> unlawful.  Please reply to the message immediately by informing the
> sender that the message was misdirected.  After replying, please
delete
> and otherwise erase it and any attachments from your computer system.
> Your assistance in correcting this error is appreciated.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
>
to:[email protected]<to%3ASprinklerforum-request@
fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4861 (20100212) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4861 (20100212) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3ASprinklerforum-request@
fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.  Your assistance in correcting this 
error is appreciated.  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to