Here's the conclusion (well sort if concluded) from last April:

From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Friday, April 17, 2009 10:28 AM
To: [email protected]
Subject: RE: IMC, IPC and nail plates


IPC 2006
305.8 Protection against physical damage. In concealed locations where
piping, other than cast-iron or galvanized steel, is installed through holes
or notches in studs, joists, rafters or similar members less than 1.5 inches
(38 mm) from the nearest edge of the member, the pipe shall be protected by
shield plates.
Protective shield plates shall be a minimum of 0.062-inch-thick (1.6 mm)
steel, shall cover the area of the pipe where the member is notched or
bored, and shall extend a minimum of 2 inches (51 mm) above sole plates and
below top plates.

IMC 2006
305.5 Protection against physical damage. In concealed locations where
piping, other than cast-iron or steel, is installed through holes or notches
in studs, joists, rafters or similar members less than 1.5 inches (38 mm)
from the nearest edge of the member, the pipe shall be protected by shield
plates. Protective shield plates shall be a minimum of 0.062-inch-thick (1.6
mm) steel, shall cover the area of the pipe where the member is notched or
bored, and shall extend a minimum of 2 inches (51 mm) above sole plates and
below top plates.

Here's how we deal with this. 
We nail plate the sole plates(one or up to 3 depending on the construction,
houses with gypcrete floors typically have an extra plate or two depending
upon how thick the gyp is.) and slip a steel sleeve around the riser coming
thru the plate.(We find we have enough scrap pipe around to keep a constant
supply of 8" sleeves. We use 8" because we have base moldings here that go
to 10" high on occasion.)

Most walls we see are double plates at the top. Only the upper plate is the
actual "Top Plate" the second plate has a name I forget right now. Any way
we nail plate both plates and have our "Nominal" 2" below the top plate.
We've never had any problem with doing this from any inspector.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


I'll add there seems later in the discussion to be some disagreement whether
IPC or IMC applies to fire sprinkler system.  One highly esteemed forumite
says no can't use IMP or IMC as fire sprinklers are not covered in the scope
of those doc.   Another highly esteemed forumite says yes but through IFC
102.7 or IFC 102.8 for matters not provided for and a nationally recognized
standard.  The debate goes on... 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest Wilson
Sent: Monday, February 15, 2010 5:47 PM
To: [email protected]
Subject: RE: CPVC and Nail plates

This came up on the Forum a few months ago.
I think it is not in NFPA standards but found in building codes.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Monday, February 15, 2010 5:14 PM
To: [email protected]
Subject: CPVC and Nail plates

Does anyone know if nail plates are required by code for CPVC pipe?
We do it as a safeguard but I had a salesmen ask me and I could not find
it in NFPA.
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to