Here's the conclusion (well sort if concluded) from last April:

From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
McMahon
Sent: Friday, April 17, 2009 10:28 AM
To: [email protected]
Subject: RE: IMC, IPC and nail plates


IPC 2006
305.8 Protection against physical damage. In concealed locations where
piping, other than cast-iron or galvanized steel, is installed through
holes or notches in studs, joists, rafters or similar members less than
1.5 inches
(38 mm) from the nearest edge of the member, the pipe shall be protected
by shield plates.
Protective shield plates shall be a minimum of 0.062-inch-thick (1.6 mm)
steel, shall cover the area of the pipe where the member is notched or
bored, and shall extend a minimum of 2 inches (51 mm) above sole plates
and below top plates.

IMC 2006
305.5 Protection against physical damage. In concealed locations where
piping, other than cast-iron or steel, is installed through holes or
notches in studs, joists, rafters or similar members less than 1.5
inches (38 mm) from the nearest edge of the member, the pipe shall be
protected by shield plates. Protective shield plates shall be a minimum
of 0.062-inch-thick (1.6
mm) steel, shall cover the area of the pipe where the member is notched
or bored, and shall extend a minimum of 2 inches (51 mm) above sole
plates and below top plates.

Here's how we deal with this. 
We nail plate the sole plates(one or up to 3 depending on the
construction, houses with gypcrete floors typically have an extra plate
or two depending upon how thick the gyp is.) and slip a steel sleeve
around the riser coming thru the plate.(We find we have enough scrap
pipe around to keep a constant supply of 8" sleeves. We use 8" because
we have base moldings here that go to 10" high on occasion.)

Most walls we see are double plates at the top. Only the upper plate is
the actual "Top Plate" the second plate has a name I forget right now.
Any way we nail plate both plates and have our "Nominal" 2" below the
top plate.
We've never had any problem with doing this from any inspector.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


I'll add there seems later in the discussion to be some disagreement
whether IPC or IMC applies to fire sprinkler system.  One highly
esteemed forumite says no can't use IMP or IMC as fire sprinklers are
not covered in the scope
of those doc.   Another highly esteemed forumite says yes but through
IFC
102.7 or IFC 102.8 for matters not provided for and a nationally
recognized standard.  The debate goes on... 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest
Wilson
Sent: Monday, February 15, 2010 5:47 PM
To: [email protected]
Subject: RE: CPVC and Nail plates

This came up on the Forum a few months ago.
I think it is not in NFPA standards but found in building codes.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Monday, February 15, 2010 5:14 PM
To: [email protected]
Subject: CPVC and Nail plates

Does anyone know if nail plates are required by code for CPVC pipe?
We do it as a safeguard but I had a salesmen ask me and I could not find
it in NFPA.
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to