I think what #3 is saying is that let's say you have a 6" underground, but
reduce at the riser to 3" because that is all of the system demand you have,
you can flow a 3" open outlet at the riser to flush the underground, and
that is equal to the maximum flow rate available to the system under fire
conditions. It will create the maximum velocity in the underground pipe that
that pipe will ever see, unless it breaks while it's still 6" or the system
is altered and the riser increased in size.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Subject: Underground flushing velocities

NFPA 24 says the following:

 (3) Maximum flow rate available to the system under fire conditions