I don't know that Job makes a 165*bulb, likely why there isn't.

I'm not allowed to have an opinion on this, but if I did I'd think there
wouldn't be a significant difference in response and even if you mixed em in
the same room with some 165*F link heads, there'd be no material bad karma
resulting. Except YOU'd know they didn't match. I'm guessing this is a
situation where you need to match a head you can't get?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Monday, March 29, 2010 7:49 PM
To: [email protected]
Subject: RE: 165 degree glass bulb heads 

Forest,

I think the RTI on a 165F link and 155F bulb are about the same, anyway they
are both considered ordinary temperature. Intermediate starts at 175F.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, March 29, 2010 4:41 PM
To: Forest Wilson; [email protected]
Subject: 165 degree glass bulb heads 

Are there any standard spray 165* glass bulb heads available? Why are the
strut heads 165 and glass bulb 155?
I need to know if the 165s are available, if anyone knows please. 
I tried posting this earlier but I don't think it went through 
Thank you 

Forest Wilson 
Cherokee Fire 

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Forest Wilson" <[email protected]>
Date: Mon, Mar 29, 2010 3:43 PM
Subject: 500 DEGREE OVEN
To: <[email protected]>

Probably because sprinkler water would reach temperatures in excess of 120*
(7.7.1.3.1.1) That pertains to combination systems, but I think there's a
similar requirement for standard wet systems.


Forest Wilson

Project Manager
Cherokee Fire Protection Co.
1855 Bellbrook Ave Ste C
Xenia OH 45385

PH 937-376-2333
FX 614-455-4324

visit our blog: www.cherokee-fire.blogspot.com


NOTICE: The information contained in this email is intended to be solely for
the use of the named individual or entity to which it is directed and may
contain information that is privileged or otherwise confidential. It is not
intended for transmission to, or receipt by, anyone other than the named
addressee (or a person authorized to deliver it to the named addressee). It
should not be copied or forwarded to any unauthorized persons. If you have
received this electronic mail transmission in error, please delete it from
your system without copying or forwarding it, and notify the sender of the
error by reply email or by calling Cherokee Fire Protection Co. at
888-347-3079 toll free.




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Robert
Thompson
Sent: Monday, March 29, 2010 3:36 PM
To: [email protected]
Subject: 500 DEGREE OVEN

Has anyone had a problem with installing a wet sprinkler in a high temp.
oven approx. 500 degrees.  The piping is on the exterior and a drop
sprinkler into the oven.   An FM plan reviewer stated that FM suggests
using a dry system when temps run this high.
 

Thank you 
 Robert  Thompson 

 DAKOTA 
FIRE PROTECTION 
1710 N. Washington Street 
Grand Forks ND 58206-5327 
Phone # (701) 772-8820 
Fax # (701) 772-7932 
Email [email protected] 

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to