NFPA 24 says the following:

NFPA 24: 10.10.2.1.3 The minimum rate of flow shall be not less than one of the 
following:
(1) Hydraulically calculated water demand flow rate of the system, including 
any hose requirements
(2) Flow necessary to provide a velocity of 10 ft/sec (3.1 m/sec) in accordance 
with Table 10.10.2.1.3
(3) Maximum flow rate available to the system under fire conditions





Debate is whether that means that the flow rate dictates the velocity and it 
has no absolute requirement or the minimum is 10fps.

Based on wording in the Appendix it would appear that 10fps is the desired 
minimum.

So for example I have a flow rate of 8000 gpm (fire flow per local AHJ) and the 
line size ends up being 24" Vel= 6.74 fps.  Is that acceptable per NFPA 24, 
10.10.2.1.3?  There are issues with the distance between source and pump 
suction and larger pipe equal less friction loss but also lowers velocities.

I read it that it can be less than any one of the following with 10fps being 
the minimum.   Sometimes simpler wording for non-FP types would make life 
easier.  <sigh>

Thought, comments, etc?????????

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to