Agree - if a dry sprinkler system, screwed pipe should be used.

John


John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, March 29, 2010 5:38 PM
To: [email protected]
Subject: RE: 500 DEGREE OVEN

Might have trouble with the grooved gaskets....even if its just from heat 
transferred from the oven armovers to the line or main.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Robert Thompson
Sent: Monday, March 29, 2010 4:01 PM
To: [email protected]
Subject: RE: 500 DEGREE OVEN

Wouldn't a dry system be the easiest. 


Thank you
 Robert  Thompson 

 DAKOTA
FIRE PROTECTION
1710 N. Washington Street
Grand Forks ND 58206-5327
Phone # (701) 772-8820
Fax # (701) 772-7932
Email [email protected] 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Monday, March 29, 2010 3:00 PM
To: [email protected]
Subject: Re: 500 DEGREE OVEN

Now this makes more sense to me. I think Craig's CO2 (although I usually hate 
the evoking of the term CO2 I doubt if you'll have any air breathers in the 
area of protection) idea is sound, or perhaps open deluge with the same 
detection or a Protectowire type product.

On Mon, Mar 29, 2010 at 12:52 PM, Robert Thompson <[email protected]>
wrote:
> Curing oven, combustible product combustible coating. In large 
> quantity
continuous process.
>
>
> Thank you
>  Robert  Thompson
>
>  DAKOTA
> FIRE PROTECTION
> 1710 N. Washington Street
> Grand Forks ND 58206-5327
> Phone # (701) 772-8820
> Fax # (701) 772-7932
> Email [email protected]
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron 
> Greenman
> Sent: Monday, March 29, 2010 2:48 PM
> To: [email protected]
> Subject: Re: 500 DEGREE OVEN
>
> I'm feeling a little stupid. Why would you need to protect an oven?
> What kind of oven? What has to heated to 500 degrees that be in a
contained vessel? Isn't this an enclosed space where the fire would be more 
than less controlled by the consumption of oxygen? Presumably the oven itself 
isn't fuel so what's in it that;'s so hazardous? I really can't figure this one 
out.
>
> On Mon, Mar 29, 2010 at 12:43 PM, Forest Wilson 
> <[email protected]>
wrote:
>> Probably because sprinkler water would reach temperatures in excess 
>> of
>> 120*
>> (7.7.1.3.1.1) That pertains to combination systems, but I think 
>> there's a similar requirement for standard wet systems.
>>
>>
>> Forest Wilson
>>
>> Project Manager
>> Cherokee Fire Protection Co.
>> 1855 Bellbrook Ave Ste C
>> Xenia OH 45385
>>
>> PH 937-376-2333
>> FX 614-455-4324
>>
>> visit our blog: www.cherokee-fire.blogspot.com
>>
>>
>> NOTICE: The information contained in this email is intended to be 
>> solely for the use of the named individual or entity to which it is 
>> directed and may contain information that is privileged or otherwise 
>> confidential. It is not intended for transmission to, or receipt by, 
>> anyone other than the named addressee (or a person authorized to 
>> deliver it to the named addressee). It should not be copied or 
>> forwarded to any unauthorized persons. If you have received this 
>> electronic mail transmission in error, please delete it from your 
>> system without copying or forwarding it, and notify the sender of the 
>> error by reply email or by calling Cherokee Fire Protection Co. at
>> 888-347-3079 toll free.
>>
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Robert 
>> Thompson
>> Sent: Monday, March 29, 2010 3:36 PM
>> To: [email protected]
>> Subject: 500 DEGREE OVEN
>>
>> Has anyone had a problem with installing a wet sprinkler in a high temp.
>> oven approx. 500 degrees.  The piping is on the exterior and a drop 
>> sprinkler into the oven.   An FM plan reviewer stated that FM 
>> suggests using a dry system when temps run this high.
>>
>>
>> Thank you
>>  Robert  Thompson
>>
>>  DAKOTA
>> FIRE PROTECTION
>> 1710 N. Washington Street
>> Grand Forks ND 58206-5327
>> Phone # (701) 772-8820
>> Fax # (701) 772-7932
>> Email [email protected]
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to