If there is no specific requirement, the whole paragraph becomes irrelevant.   


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Denhardt
Sent: Wednesday, March 31, 2010 1:55 PM
To: [email protected]
Subject: RE: Underground flushing velocities

I agree with Roland.  Not less than one of the following.  It does not state 
pick the highest.  You can use ANY one of the procedures.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Wednesday, March 31, 2010 2:09 PM
To: [email protected]
Subject: RE: Underground flushing velocities

With all due respect, I don't see the word 'any' anywhere in 10.10.2.1.3.
I'm looking at the 2010 version, maybe older versions contain the word 'any'.

Ed Kramer
Littleton, CO


> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum- 
> [email protected]] On Behalf Of Law, Kevin W
> Sent: Wednesday, March 31, 2010 11:38 AM
> To: [email protected]
> Subject: RE: Underground flushing velocities
> 
> The key is the requirement states it shall not be less than ANY one of 
> the following.
> 
> Therefore, the very minimum flow rate will be 10ft/sec line velocity.
> 
> If your system cannot under any condition flow a minumum of 10ft/sec 
> then you would have to get a ruling from the AHJ to allow that.
> 
> Nuff said
> 
> 
> Kevin Law, PE
> Bechtel National, Inc.
> Waste Treatment Project
> Fire Protection Engineering
> Work  (509) 371-3280
> Cell    (509) 531-5715

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to