You are correct the word any does not appear in the text.  I guess my
comment was slanted from the view that in the text for NFPA 24-1995.  

"The minimum rate of flow shall be not less than the
water demand rate of the system, which is determined by
the system design, or not less than that necessary to provide
a velocity of 10 ft/s , whichever is greater."

The standard changed on the next revision to it's present
wording.........

I find that crow is best eaten while it is still warm, it sticks in your
throat less


Kevin Law, PE
Bechtel National, Inc.
Waste Treatment Project
Fire Protection Engineering
Work  (509) 371-3280
Cell    (509) 531-5715


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Wednesday, March 31, 2010 11:09 AM
To: [email protected]
Subject: RE: Underground flushing velocities

With all due respect, I don't see the word 'any' anywhere in
10.10.2.1.3.
I'm looking at the 2010 version, maybe older versions contain the word
'any'.

Ed Kramer
Littleton, CO


> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-

> [email protected]] On Behalf Of Law, Kevin W
> Sent: Wednesday, March 31, 2010 11:38 AM
> To: [email protected]
> Subject: RE: Underground flushing velocities
> 
> The key is the requirement states it shall not be less than ANY one of

> the following.
> 
> Therefore, the very minimum flow rate will be 10ft/sec line velocity.
> 
> If your system cannot under any condition flow a minumum of 10ft/sec 
> then you would have to get a ruling from the AHJ to allow that.
> 
> Nuff said
> 
> 
> Kevin Law, PE
> Bechtel National, Inc.
> Waste Treatment Project
> Fire Protection Engineering
> Work  (509) 371-3280
> Cell    (509) 531-5715

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to