The foam concentrate lines are typically dictated by the mfgr.  Only mention of 
specifics is that the foam concentrate piping NOT be galvanized.  Some of the 
concentrates can have a somewhat corrosive nature to them.  Consult the 
manufacturer of the foam you intend to use.

Foam concentrate ratio (3% or 6% are typical) are dependant on the hazard being 
protected.  Again it's best to consult with the mfgr.  Also they can tell you 
the specific design density to use and whether you need air aspirating type 
sprinklers or standard heads will be suitable.

Once you give them the MSDS on the chemical to be protected they will also tell 
you whether you need Alcohol Resistant or standard AFFF.  


 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Russell
Sent: Wednesday, April 14, 2010 2:31 PM
To: AFSA
Subject: Foam system piping

The last time I designed a foam system was over 20 years ago and I don't recall 
very much of the specifics. I used stainless steel pipe to carry the foam 
concentrate to the porportioner. I do know that it needs to be corrosion 
resistant. What I don't remember is why stainless. Was it required by the foam 
manufacturer, the project specifications or a fire code? Can someone help me 
out here? One more thing I don't remember is what type foam concentrate it was. 
Not much info, huh.

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to