In current foam design, the concentrate is only in concentrate form at the exit 
of the bladder tank as it is introduced into the system piping at the 
proprtioner.  From that point on it's only at typically 3% in concentration 
with water.  So Frans I'm not sure what kind of systems you are describing 
because most are dry or pre-action when talking about the majority of systems.  
No need for stainless pipe, welded fittings or flanges for systems which will 
be dry most of their lifetime.  Now the concentrate piping between the bladder 
tank and proprtioner is typically stainless and threaded.  But beyond that, the 
systems follow NFPA 13 or 15 for installation standrds for the most part.


CH2MHILL/SPB
Craig Prahl
8640599-4102
________________________________________
From: [email protected] 
[[email protected]] On Behalf Of Frans Stoop 
[[email protected]]
Sent: Saturday, April 17, 2010 3:04 PM
To: [email protected]
Subject: RE: Foam system piping

Russell,

The problem with foam concentrate is that it always tends to creep
out of the piping and equipment, passing along seals, fitting threads
etc. This behavior is caused by its zero surface tension.
To keep it in the piping as much as possible we usually specify
welded pipe connections or connections with positive pression on the
seals only, like flanges.
Groove couplings are to be avoided. Threaded fittings to be fitted
with hard sealing Loctite and for diameters not exceeding 1 inch only.
And the stuff still keeps creeping out along valve stems etc.
Small foam concentrate spills and leaked droplets on the outside of
pipe and equipment dry out and become a thick and corrosive
salt-solution. After a few years this wet salt is able to erode all
kinds of paint (including epoxy paint!), ordinary steel and cast iron.

For aircraft hangars we use to design and specify for a lifetime of
25 years. According to our experience only stainless steel piping and
stainless steel or chrome plated bronze valves survive that lifetime
when in direct contact with foam concentrate. Concentrate spills are
easily wiped or washed off with a cloth, even after a year or more,
and the system keeps looking good.

Yours sincerely,

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112

At 16:53 14-4-2010 -0400, you wrote:
>A very, very large airport terminal. Not military.
>
>Russell Rewis
>Brown Automatic Sprinklers, Inc.
>107C Hemlock Street
>Valdosta, Georgia 31601
>229-244-8130
>[email protected]
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of
>[email protected]
>Sent: Wednesday, April 14, 2010 4:41 PM
>To: [email protected]
>Subject: RE: Foam system piping
>
>So what's the application is we may ask?  Just curious?

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to