My concern is that I may be overlooking a standard or code or something that
might turn around and bite me. My next move will be as you suggest, call the
guy that makes it! Glad you brought up the alcohol resistant feature.
Thanks Craig.

Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, April 14, 2010 3:42 PM
To: [email protected]
Subject: RE: Foam system piping

The foam concentrate lines are typically dictated by the mfgr.  Only mention
of specifics is that the foam concentrate piping NOT be galvanized.  Some of
the concentrates can have a somewhat corrosive nature to them.  Consult the
manufacturer of the foam you intend to use.

Foam concentrate ratio (3% or 6% are typical) are dependant on the hazard
being protected.  Again it's best to consult with the mfgr.  Also they can
tell you the specific design density to use and whether you need air
aspirating type sprinklers or standard heads will be suitable.

Once you give them the MSDS on the chemical to be protected they will also
tell you whether you need Alcohol Resistant or standard AFFF.  