You need to tread carefully on this one.  2006 IBC 1020.1.2 states 
"Penetrations into and OPENINGS THROUGH ...". Peel back to 1020.1 which 
states "Interior exit stairways and interior exit ramps shall be 
enclosed with fire barriers constructed in accordance with Section 706". 
Peel back to 706.6 which states "Openings in a fire barrier shall be 
protected in accordance with Section 715". 715 protects openings with 
opening protectives - fire doors, shutters, or fire-rated glazing. Tough 
running and protecting sprinkler piping through those. (Oh, and openings 
are not allowed in fire-rated glazing unless tested and listed, just in 
case...)

Bottom line, in my opinion, sprinkler and standpipe piping can run into 
and out-of the enclosure as many times as required with 
through-penetration protection, but, not through.

Dan Kaczor
Plans Examiner, Building Official (and sometimes Architect)

ps: Haven't posted in years, I learn a lot from ya'll by keeping my 
mouth shut with ears and eyes wide open.