Yes.

The read from NFPA is (not quoted) UP TO TWO HEADS in the most
demanding compartment(s) for 13D and the same but UP TO FOUR HEADS in
a 13R. I don't know if you reviewed it and it was a while ago but up
in the U District I did a five unit condo that on the floor and
directly  above the riser room had a three head compartment, and
directly above that a two-head compartment and everything else with
one head compartments. You guys got a calc for the three head one
because it had the most heads even though closest to the riser (2nd
floor), the two head one (3rd floor) because it was at a higher
elevation than the three header although also directly above the
riser, and a single head calc from a compartment also on the 3rd floor
because it was the farthest away from the riser. I use this all the
time in class because it's a perfect, and simple example of why you
sometimes need multiple calcs.

On Fri, May 28, 2010 at 11:39 AM, Richardson, R
<[email protected]> wrote:
> I had always thought that both NFPA 13R and 13D required a minimum two head 
> calculation.
>
> For various reasons we were actually reading it today and notice that there 
> does not appear to be a minimum number of heads to calc, just calc. how many 
> heads are in a compartment.
>
> We have an apartment whose units have 1 head per compartment, is it 
> acceptable to do a 1 head calc for 13R?
>
> Thanks,
>
> Rich Richardson
> Seattle Fire Department
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to