Good Lord!!!! A rational rationale. Kudos.

On Wed, Jun 9, 2010 at 1:48 PM, Eggen, Clarence (Dale)
<[email protected]> wrote:
> Sleeves are being provided in every concrete wall throughout the facility 
> that I am currently working on.  Early in the project, a study was done to 
> determine where the sprinkler piping would enter each room and a sleeved 
> opening was provided.  Coring holes in the concrete walls is almost 
> impossible, as the core boring is not allowed to cut more than one rebar.  
> The rebar in most walls is 4-inch on-centers in both direction and there are 
> two or more rebar mats in each wall.  The sprinkler subcontractor has been 
> able to route the piping such that core holes have not been required.
>
> Dale Eggen, PE
> BNI
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Wednesday, June 09, 2010 1:40 PM
> To: [email protected]
> Subject: RE: Sleeve
>
> Ok, let's get real, Architects are the ones who typically require the sleeves 
> in their walls.  Sleeves are prettier than ghastly, ravaged wall openings 
> created by savage, unbathed contractors because it's written to be that way 
> in the spec.  Stop arguing about it.
>
> Many times things like sleeves can be based on a lot of issues, the client's 
> or Underwriter's requirements or the A/E's bad experience with Bubba, Enus 
> and Lothar Fire Protekshn Speshulists.  Each bad experience tends to add at 
> least 5 pages to the spec to cover these issues for the next go-round.      ;)
>
> But seriously, there are cases where the sleeves are a requirement and times 
> when they are just a preference.
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Chris Cahill
> Sent: Wednesday, June 09, 2010 4:04 PM
> To: [email protected]
> Subject: RE: Sleeve
>
> OK so why would they cut the hole for the sleeve any different?  And doesn't
> the pipe create the same seal?  We tend to use pipe with few holes in them.
> Guess I can't speak for others, lol.
>
> And actually our pipe is hanging long before the sheet rockers get there.
> New construction accounting for the vast majority of work.   And sheetrock
> whether metal or wood studs makes up the vast majority of the walls. And
> block would usually be there before our pipe so again to the question above
> why would they cut the hole for the sleeve any different? And...And...And...
>
> What I hear is instead of requiring a sleeve they could be spec'ing a
> performance standard for the annular space around the penetration. Then
> whoever makes the hole takes care to not use the hammer.
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
> Email: [email protected]
>
> Mail: P.O. Box 69
>        Waverly, MN 55390
>
> Location: 4439 Hwy 12 SW
>              Waverly, MN 55390
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, June 09, 2010 2:43 PM
> To: [email protected]
> Subject: RE: Sleeve
>
> Yes you have no shame, how dare you even ask!
>
> But the answer is.....  wait for it.......... The sleeve.
>
> Otherwise when penetrating a block or stud wall there is an exposed cavity
> if you have allowed any space between your pipe and the wall material.  Hard
> to describe here in words.  You're assuming that all contractors cut nice
> clean holes no bigger than 1/32" larger than their pipe and there is no
> space around the pipe.  Most put holes in concrete with a sledge hammer or
> use the sawzall to cut their holes in sheet rock if they don't also use a
> hammer in that application and the hole is about 3 times bigger than it
> needs to be.
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Mark Sornsin
> Sent: Wednesday, June 09, 2010 3:33 PM
> To: [email protected]
> Subject: RE: Sleeve
>
> (o.k. I know I'm going to regret asking this - but I have no shame)
>
> What provides the solid interior surface when a sleeve penetrates a block or
> stud wall?
>
>
> Mark A. Sornsin, PE | Fire Protection Engineer
> Ulteig Engineers, Inc. |Fargo, ND
> Direct:    701. 280.8591 | www.ulteig.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, June 09, 2010 2:19 PM
> To: [email protected]
> Subject: RE: Sleeve
>
>
> In walls they can provide a solid interior surface when penetrating block or
> stud walls and provide closure to the wall cavity.  They also provide for a
> space between the pipe and wall for packing if necessary when providing
> certain UL listed penetrations at rated walls and partitions.
>
> Sleeves are at times a requirement in walls or floors of particular
> construction types in order to maintain the assembly's rating.  UL details
> require sleeves for penetrations in many cases.
>
> ject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________